Good afternoon everyone-
I apologize if I leave anything out, but I'll try to paint the best picture I can of our situation.
We just lost a control board on our NEW ABB DCS 800 DC drive. I installed it about 5 days ago.
We replaced it because we were unable to communicate any longer on our previous (Ebay used) drive from the HIM to either port on our AB 1736.
Both of those conclusions were reached with their respective tech support and doing the "required" troubleshooting. Happy to go into either one of those failures more, just wanted to make sure to get the important info.
There is no line reactor installed. After trying to order one at the same time as the drive, since the last one didn't have one either, the filter was 1.5-2 weeks out, so against everyones advice, they decided to run it "Temporarily"
They're looking for a different answer of why we lost this new drive than "We should have gotten a line reactor". They're thinking is that the last used AB drive from circa '95 I believe, lasted 6 months, and the new one only lasted about 5 days.
What I'm hoping to get is more possibilities to look into of what could have taken out the drive, and also, other ideas or best practices for better protecting this drive in the future. currently there is no Line Reactor, Line contactor, or armature fusing, which I hope to change. This is my first DC drive of this size, and although I've done alot of AC drives, I thought I might ask the professionals. Depending on who I get on the phone, Tech Support hasn't been the most helpful
I'll also add that the fault on the new drive was a "Low Mains Voltage", which was reading 2v on the drive, but measuring normal with my meter. I'll also add that it faulted out another drive on the same extrusion line with a 0v fault, but that one reset.
Thanks to everyone for taking the time out of your day to read this, and I look forward to any responses/questions.
Work safe everyone-
I apologize if I leave anything out, but I'll try to paint the best picture I can of our situation.
We just lost a control board on our NEW ABB DCS 800 DC drive. I installed it about 5 days ago.
We replaced it because we were unable to communicate any longer on our previous (Ebay used) drive from the HIM to either port on our AB 1736.
Both of those conclusions were reached with their respective tech support and doing the "required" troubleshooting. Happy to go into either one of those failures more, just wanted to make sure to get the important info.
There is no line reactor installed. After trying to order one at the same time as the drive, since the last one didn't have one either, the filter was 1.5-2 weeks out, so against everyones advice, they decided to run it "Temporarily"
They're looking for a different answer of why we lost this new drive than "We should have gotten a line reactor". They're thinking is that the last used AB drive from circa '95 I believe, lasted 6 months, and the new one only lasted about 5 days.
What I'm hoping to get is more possibilities to look into of what could have taken out the drive, and also, other ideas or best practices for better protecting this drive in the future. currently there is no Line Reactor, Line contactor, or armature fusing, which I hope to change. This is my first DC drive of this size, and although I've done alot of AC drives, I thought I might ask the professionals. Depending on who I get on the phone, Tech Support hasn't been the most helpful
I'll also add that the fault on the new drive was a "Low Mains Voltage", which was reading 2v on the drive, but measuring normal with my meter. I'll also add that it faulted out another drive on the same extrusion line with a 0v fault, but that one reset.
Thanks to everyone for taking the time out of your day to read this, and I look forward to any responses/questions.