Connecting a panelview plus to a second network

stu

Member
Join Date
Aug 2005
Location
England
Posts
772
Hi guys
Just a thought
I have a pvp on a 192.168.1.xxx network if I wanted to add a the screen to a second network say 192.168.0.xxx could I change the subnet on the hmi ?
It’s just a thought ? Can you see any issues

EFCCE58E-3D19-45CF-BF76-1475C3C6036C.png
 
The 192.168.1.xxx subnet needs a router/gateway that routes packets to the 192.168.0.xxx but this is a task of a network administrator rather than a plc/hmi programmer, then on this screen config you will need to put the 192.168.0.xxx IP of the second PLC and the IP of the new router/gateway

Another solution is to physically join both networks and change all the subnet masks to 255.255.254.0
 
Last edited: