vfd speed controlled by a thermistor

Does the drive have PID capability?

For a cooling tower application, shouldn't you be using the water temperature as the feedback? You would also like to monitor/calculate the outdoor air wetbulb temperature to bound your setpoint.

A cooling tower can be used to cool the water to perhaps 5-7degrees higher than ambient wetbulb temperature, but not lower. SO if the ambient wetbulb is 78F, you should be able to cool the water to ~83F. If the wetbulb is 85F, you will not be able to cool the water to 85F no matter how hard the fans run.
 
The vfd does have PID capability.

I am not the engineer on this job and I am not familiar with all the details on cooling towers. I am basically making sure they have the hardware to do what they want to do.

But thanks for your suggestions. I may be able to suggest improvements to them along the way.

Also. This motor is only a 3hp so I believe it is some auxiliary motor and not used for the main cooling action
 

Similar Topics

Hello, I am trying to setup on plc so If I enter 60 jph (job per hour) it will send the vfd hertz based on what jph is entered by...
Replies
2
Views
152
Working on 2 VFDs for two motors, they follow any speed command when local and in hand. Once I try to give a Speed reference from my PLC they both...
Replies
10
Views
2,178
Hello, So I was asked to turn up the speed on a VFD to allow a carriage to move a little bit faster and avoid getting stuck. Im not sure the exact...
Replies
2
Views
727
I'm trying to figure out how to read the actual speed reference value from the move blocks, writing to a DB that is being sent to the VFD. For...
Replies
5
Views
2,630
I don't understand how vfd detects speed when we are running in open loop control (sensorless). For me only possible way; during auto tuning it...
Replies
4
Views
2,646
Back
Top Bottom