siemens sinamics control unit CU250S-2-USS

Hasitha

Member
Join Date
Dec 2015
Location
colombo
Posts
44
Dear Team,

I need to increase the maximum speed of my drive upto 60 HZ. and sadly im stuck with some parameter. Below parameters are already changed and still im facing the same problem. :(

p0310- Rated motor frequency
p1082- Maximum speed in rpm

The issue which i drive upto this matter is fault F7901 when i increased my motor speed into maximum(upto 50 HZ). So i thought that if i adjust my maximum frequency upto 55HZ i can easily run my motor in 50Hz.

Plz advice???

Also p0100-IEC/NEMA Motor stds is at 0 .(Europe 50 Hz)

May i put it into 1 or 2 (Means NEMA motor 60 hz) ??????
 
Did you already check what that fault F7901 means? And about those motor parameters. Those are rating values which are stated in the type plate in the motor. You cannot change them. If you want to increase output freq. of the drive you have to find parameter "maximum output freq" or something like that.

e:forget to mention but of course you have to choose are you using 50hz or 60hz rating values and that depends what is your supply voltage.
 
Last edited:
Did you already check what that fault F7901 means? And about those motor parameters. Those are rating values which are stated in the type plate in the motor. You cannot change them. If you want to increase output freq. of the drive you have to find parameter "maximum output freq" or something like that.

e:forget to mention but of course you have to choose are you using 50hz or 60hz rating values and that depends what is your supply voltage.

Dear Mara,
I know that i need to increase the maximum frequency and that what im asking what is the relavant parameter. Also F7901 means motor overspeed and manual says i need to increase the P1082 (means maximum speed)
Since im in srilanka here we use 50 HZ
 
Change P310 back to 50hz
Now change P1082 and P2000 to 60
your motor will now go to 60hz


Dear JRW,

i alredy changed p1082 and i cant find p2000 on my drive. I think its because that it is on acces level 2 stage.
So please be kind enough to explain me how to access for p2000( Reference speed reference frequency) 🤞🏻 🤞🏻:oops::oops:
 

Similar Topics

Hello sameone have Beckhoff PLC Siemens Sinamics V90 configuration example?
Replies
0
Views
96
Hello, I use a Siemens Sinamics G120C inverter in combination with a S7-1200 cpu. I use the Main Setpoint with the Providrive option and send...
Replies
8
Views
690
I have G120 with Firmware version V4.7.13. In the TIA project, I have version V4.7.10. I would like to install new firmware HSP in my project. I...
Replies
2
Views
1,796
Hi , A little off topic , hope you don't mind I have a Siemens Sinamics V20 Inverter On a 0 - 10 v analogue input as a speed reference...
Replies
4
Views
1,073
Good day Wanting to learn about servos, I bought from Ebay, a USED Siemens Sinamics S210 servo drive with the 1FK2130-2AG00-2SA0 motor. The unit...
Replies
2
Views
1,511
Back
Top Bottom