Replace relay with sinking output (non)
I’ve got some devices that are triggered by shorting pins to common. There is 24 volts on each pin and right now I am using a relay output card in a SLC rack to do this now.
I think this is called BCD, as you can select a number up to 127 by combining relays. I am putting together a new system with Point IO hardware and the most relay outputs I can find for the 1734 series is a 4 relay output card. So i would need 2x output cards per device which would add up quickly. I was wondering if a sinking output card would do the same thing. It’s my understanding that a sinking output would pull the output to the common terminal. Anyone have any experience or advice on this? Title was supposed to be NPN, auto correct got me again. |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
solid state outputs have some leakage so you might have to add pull down resistors to compensate for that.
__________________
≈ There are 2 kinds of people in the world... (1) Those that can derive answers from incomplete Data |
![]() |
![]() |
#3 |
Lifetime Supporting Member
|
Actually changing over to a sinking output would be good for this, and the transistor outputs usually last longer than the relays in the existing cards. Plus if this is in an office or in your house the noise of relays clicking can be enough to turn the PLC off until you get DC outputs. [Speaking from experience - the first PLC I setup for the lights on my Christmas tree was all relay outputs, had to shut that off within 15 minutes]
Just buy some resistors and add them from the start as TheWaterboy says.
__________________
ivanovaautomation.com Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors |
![]() |
![]() |
#4 | |
Lifetime Supporting Member
![]() ![]() Join Date: Apr 2019
Location: Oklahoma
Posts: 54
|
Quote:
Anyone have experience with using 12v devices on the 1734-OV4E? It says 10-28 volts for input and the minimum voltage for an output being 10v. I am using a Patlite voice annunciator which works on 24vdc but the PA (separate device) uses 12VDC and uses the same type of trigger, shorting the input pins to common. |
|
![]() |
![]() |
#5 | |
Lifetime Supporting Member
|
Quote:
I use 2 cards of DC outputs with my 12V solar batteries to control 12V lights with no problem. Plus one NPN card does control 12V and 24V circuits with the 0V tied together from the batteries and 24V power supply. I even had a ML1400 with DC IO ready to go to "interfere" with the way my SUV controlled all the lights, and add a GetOutOfMyWay flashing mode - but a drunk driver totaled it for me before I got to until it and the new SUV has a weird setup for parking and taillights (no separate bulbs, it gives the turnsignals & brake lights 6.5 volts to light them up dimmer) The reply above about NPN output devices can be activated by the wire grounding out is a valid issue, but I deal with a lot of machinery from Europe & Asia and they ALL use NPN exclusively - the engineers all think NPN devices respond faster so that's what they use, but when I point out the PLC in the machine only scans once every 0.05 seconds (1/20 second) a device responding 0.0002 seconds quicker is not going to be noticed 99.99% of the scans.
__________________
ivanovaautomation.com Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors |
|
![]() |
![]() |
#6 |
Lifetime Supporting Member
![]() ![]() Join Date: Apr 2019
Location: Oklahoma
Posts: 54
|
Was wondering how the wiring would work if I was using a 1734-OV8 output card. If the power comes from the backplane would I need to use one of the 1734-FPD modules to separate it from the 24v on the backplane?
|
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Feb 2018
Location: New York State
Posts: 75
|
I've been using transistor outputs with 6mm slim relays. The cost of a transistor output card and 6mm relays combined is usually less than a relay card by itself. Custom interlocks, power feeds, and voltage differences are far more flexible. The control box real estate taken by the relays is minimal. The usual current draw is up to 6A for each relay.
|
![]() |
![]() |
#8 |
Member
|
Rethink what you are doing
Sinking Output / Inputs are frowned on in the industry a ground fault can cause an inadvertent input to be on and cause problems in the control In all cases it would try and avoid sinking inputs I have seen many problems with them The BCD you talked about is ( Binary Coded Decimal ) it’s only a way of displaying a number in your case 0 to 127 lower 7 bits on. Another common way they display a number in ASCII string Just keep in mind with all computer data you must know how to understand the bit pattern to understand the word / number If you are having problems with the relay contacts try switching to Gold Plated contact relays they are designed for low current applications, they self clean when the relay pulls in. most relay contacts used today are cadmium they require a larger current flow to pass through and can have problems with very low currents |
![]() |
![]() |
#9 |
Lifetime Supporting Member
|
Yes, either need a bank of 8 interposing relays for the -OV8 or isolated inputs.
Unless you have the RemoteIO card using 8 mini-DIN mount relays would be less costly. The cards I use are in SLC racks.
__________________
ivanovaautomation.com Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Triac versus Relay output card | CeeDee | LIVE PLC Questions And Answers | 6 | February 27th, 2015 03:29 AM |
What is a Test Output on a Safety Relay? | Bbarnett | LIVE PLC Questions And Answers | 8 | January 18th, 2015 02:53 PM |
Interposing relays | Malador | LIVE PLC Questions And Answers | 23 | March 2nd, 2013 01:52 AM |
Encoder output types | Orn Jonsson | LIVE PLC Questions And Answers | 10 | May 9th, 2007 05:25 PM |
Control Logix relay output trouble | LED | LIVE PLC Questions And Answers | 13 | September 16th, 2003 02:59 PM |