![]() ![]() ![]() ![]() This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc. |
||
![]() |
![]() |
#1 |
Member
|
![]()
Hi, I'm very new to PLC's. I'm trying to understand a program that someone else has written. I having trouble understanding the LIM (limit test)I understand where the High Lim and Low Lim come from, but where does the value for the 'Test' come from. I'm looking at a program that has
low lim 4000 4000< Test I:7.0 12234< High Lim 20000 20000< I understand that I:7.0 is an address input but, where does the 12234 come from. Is that a value from the input? Could you please explain the 'Test' part of the LIM (limit test). Thanks ~Snide |
![]() |
![]() |
#2 |
Member
|
The "12234" is the current value of input word I:7.0
This rung is true because: 4000 < 12234 < 20000 Or, verbally, the "Test" value is between the low and high limits.
__________________
"Invention is 1% inspiration and 99% perspiration - Edison." This explains why so many engineers smell so bad... ![]() |
![]() |
![]() |
#3 |
Lifetime Supporting Member
|
A copy of RSLOGIX instruction help. From the help file
LIM [Limit Test] Use with processorsSLC 5/02SLC 5/03SLC 5/04SLC 5/05 All MicroLogix Example of Instruction(Parameters shown are examples only, your data will vary.) Description Use the LIM instruction to test for values within or outside a specified range, depending on how you set the limits. Entering Parameters Depending on how you define the Test parameter, the Low and High Limit parameters can be a word address or program constant. See below. Test Low Limit High Limit Constant Word Address Word Address Word Address Constant or Word Address Constant or Word Address True/False Status of the Instruction If the Low Limit has a value equal to or less than the High Limit, the instruction is true when the Test value is between the limits or is equal to either limit. If the Test value is outside the limits, the instruction is false. If the Low Limit has a value greater than the High Limit, the instruction is false when the Test value is between the limits. If the Test value is equal to either limit or outside the limits, the instruction is true. Related Topics Comparison Instructions Addressing Help Rockwell Software 2005
__________________
Mickey If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else. ----- Chinese Proverb Last edited by Mickey; October 20th, 2005 at 11:47 AM. |
![]() |
![]() |
#4 | |
Member
|
Quote:
I have seen people examining the logic go crazy trying to understand this... Good one, Mickey. In my race to reply to this, I took the easy answer. Yours examines the "complete" answer.
__________________
"Invention is 1% inspiration and 99% perspiration - Edison." This explains why so many engineers smell so bad... ![]() |
|
![]() |
![]() |
#5 |
Member
|
Thanks, I think one day maybe I'll understand this stuff ~Amy
|
![]() |
![]() |
#6 |
Lifetime Supporting Member
|
Jimmie ohio,
Not my words, I cut and pasted the software's help file.
__________________
Mickey If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else. ----- Chinese Proverb |
![]() |
![]() |
#7 |
Member
|
I was wonder about SCP (scale with parameters). Maybe you could expain the rung I have. the program is for reading data from a radar on a liquid tank. like i posted before for the lim
4000 <4000 I:7.0 <12234 20000 <20000 and on the same rung SCP input I:7.0 <12234 input min. 4000 <4000 input max. 20000 <20000 scaled min. 2.0 <2.0 scaled max. 119.0 <119.0 output F25:3 <62.21113 how do you calc. by hand to get 62.21113?? how do you choose scaled min and max?? My boss wants me do use this program for 8 other tanks and i want to make sure I'm doing this stuff right. I read the help on RSlogix 500, but I need more help. Sorry for all the questions. |
![]() |
![]() |
#8 |
Member
|
The SCP instruction calculates the constants for and executes the standard equation for a line:
Code:
y = mx + b Code:
m slope of the line b line offset from the origin Code:
m = (scaled max - scaled min) / (input max - input min) Code:
b = scaled max - (input max * m) I hope this helps. Keith Last edited by kamenges; October 20th, 2005 at 01:47 PM. |
![]() |
![]() |
#9 |
Lifetime Supporting Member
|
Raw Data = value at I:7.0
(((raw data - min raw data)/ max range)* Engineering units max value-min value)+offset. ie. ((( 12234-4000)/16000)*119-2)+2=62.21113 The min and max value are the scaling of your Transmitter at the tank ie 4-20ma= 2 to 119 inches Hope this helps Kamenges you type faster then I do
__________________
Mickey If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else. ----- Chinese Proverb |
![]() |
![]() |
#10 |
Member
|
Thank you, this helps ~Amy
|
![]() |
![]() |
#11 |
Lifetime Supporting Member
|
All AB manuals can be found here:
http://literature.rockwellautomation..._category.hcst SLC500 Instruction Set Reference: http://literature.rockwellautomation...m001_-en-p.pdf MicroLogix 1200 and 1500 Instruction Set Reference: http://literature.rockwellautomation...m001_-en-p.pdf Micrologix 1000 Instruction Set Reference: http://literature.rockwellautomation...m003_-en-p.pdf Last edited by TConnolly; October 20th, 2005 at 02:17 PM. |
![]() |
![]() |
#12 |
Member
|
This is quick:
% = (Input-Min)/(InputMax-InputMin) = (12234-4000)/(20000-4000) = .514 NewValue =(%*(ScaledMax - ScaledMin))+Scaledmin = (.514*(119-2))+2 = 62.12 |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Problems with Siemens CP340 RS232C communication | Borte | LIVE PLC Questions And Answers | 12 | December 26th, 2019 04:23 PM |
LogixPro and the LIM Instruction | mrmss | LIVE PLC Questions And Answers | 6 | September 24th, 2005 03:28 PM |
Information about TYPE TEST MDB? | Platootod | LIVE PLC Questions And Answers | 3 | December 2nd, 2004 10:23 AM |
PID - MicroLogix Temperature Control | Peter Nachtwey | LIVE PLC Questions And Answers | 112 | October 11th, 2004 12:18 PM |
Test equipment | ranjana | LIVE PLC Questions And Answers | 1 | November 10th, 2002 06:30 AM |