Point IO Cable Length
Hi all,
I am planning on installing a AB 1794 point IO system using the ethernet 1794-AENT and 7 IO modules connected to a compactlogix L35E. The point IO will be up to 200m from the logix,will this work at this distance,and is there a recommended cable type(cat 5,5e,6)Thanks.. |
![]() |
![]() |
#2 |
Member
|
Typically shielded CAT 5e is recommended. I have in my notes (I'm sure I got it from an AB or standard ethernet recommendation as I didn't cite a source) that the maximum length is 100 meters.
If you need to run 200m then the recommended solution is to use fiber converters. Check out the 1783-ETAP1F or 1783-ETAP2F.
__________________
An expert is a man who has made all the mistakes which can be made in a very narrow field. --Niels Bohr as quoted by Edward Teller |
![]() |
![]() |
#3 |
Lifetime Supporting Member + Moderator
|
The distance you can run twisted-pair Ethernet is an ordinary limit of Ethernet technology; it's not vendor-specific to A-B. 200 meters of twisted-pair wire will not support an Ethernet link.
You need a switch or repeater in the middle of the run, or you need to run another type of media. Typically long runs are done with fiber optic media and a media converter. I like these units from N-Tron: http://www.n-tron.com/products_sub.php?type=MC |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Nov 2009
Location: Ontario
Posts: 37
|
Thanks for the replies.Looks like fibre optic is the way to go. When you set these up in RSlogix 5000 do you still map the 1794-AENT to the ethernet port or the fibre converter?
|
![]() |
![]() |
#5 |
Lifetime Supporting Member + Moderator
|
The IP infrastructure is transparent to RSLogix 5000; all it knows about is the 1734-AENT adapter out there.
There could be Ethernet cable, fiber-optics, WiFi, cable modems, cell phones, or carrier pigeons in between. As long as the packets arrive in a timely fashion, the controller doesn't know what carries them. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Omron Ethernet/IP to AB Point IO | AndrewY | LIVE PLC Questions And Answers | 1 | August 26th, 2009 08:17 AM |
Encoder Cable Length | BryanG | LIVE PLC Questions And Answers | 7 | December 12th, 2007 04:37 AM |
A-B point to point cable | jseavers | LIVE PLC Questions And Answers | 2 | July 10th, 2007 07:42 PM |
OT - Cable length KUKA Robot | MartB | LIVE PLC Questions And Answers | 1 | June 14th, 2007 10:31 AM |
RS5000 adding new point IO module | jim767 | LIVE PLC Questions And Answers | 2 | November 16th, 2006 07:20 AM |