Hi,
I am trying to use the SEND command to pass a block of data across an ethernet network.
There are a bunch of PLC's on this network and most have blank routing tables, which is more than likley my problem. I can use the send problem without issue if the ethernet IP card is node 0 on the PLC however when it's not node 0 I cannot get the data to send (error #1005). Setting up a routing table on the PLC (I set the ethernet card to network 1) I still get the same error.
Is there any way to send from Network 1 to the default network (0) on the other PLC without setting up the routing table in the destination (there's a lot of PLC's on it currently running active communications so giving it a routing table may cause downtime).
Send configurations I've tried:
Mov &40 D1980 Mov &40 D1980
Mov #0000 D1981 Mov #0001 D1981
Mov #FE00 D1982 Mov #FE00 D1982
Mov #0700 D1983 Mov #0700 D1983
Mov #0000 D1984 Mov #0000 D1984
PLC 1 (Destination) *.*.*.254 - CJ2 Ethernet card is built in
PLC 2 (Source 1) *.*.*.001 - CJ2 Ethernet card is built in (send works)
PLC 3 (Source 2) *.*.*.111 - CS1 Ethernet card is node 4, network 1 (send does not work)
Oh and using network configurator I can poll to and from PLC1 to PLC3 so the communication settings are ok for EtherentIP coms... but not FINS.
I am trying to use the SEND command to pass a block of data across an ethernet network.
There are a bunch of PLC's on this network and most have blank routing tables, which is more than likley my problem. I can use the send problem without issue if the ethernet IP card is node 0 on the PLC however when it's not node 0 I cannot get the data to send (error #1005). Setting up a routing table on the PLC (I set the ethernet card to network 1) I still get the same error.
Is there any way to send from Network 1 to the default network (0) on the other PLC without setting up the routing table in the destination (there's a lot of PLC's on it currently running active communications so giving it a routing table may cause downtime).
Send configurations I've tried:
Mov &40 D1980 Mov &40 D1980
Mov #0000 D1981 Mov #0001 D1981
Mov #FE00 D1982 Mov #FE00 D1982
Mov #0700 D1983 Mov #0700 D1983
Mov #0000 D1984 Mov #0000 D1984
PLC 1 (Destination) *.*.*.254 - CJ2 Ethernet card is built in
PLC 2 (Source 1) *.*.*.001 - CJ2 Ethernet card is built in (send works)
PLC 3 (Source 2) *.*.*.111 - CS1 Ethernet card is node 4, network 1 (send does not work)
Oh and using network configurator I can poll to and from PLC1 to PLC3 so the communication settings are ok for EtherentIP coms... but not FINS.