phuz
Member
Upgraded a PLC-5/80 today to a CLX. There are 5 physical ASB modules for a total of 10 racks. All 10 are added in the CLX tree under the DHRIO CH. A, at 115.2k baud, which is what the PLC-5 ran at. The main PLC-5 chassis was rack 0&1, so I made the ASB module rack 0 that went in it's place. The PLC-5 was end of the line, so I have a 150-ohm resistor there, and one at the other end (another ASB module). The new DHRIO is in the middle of the network, but the way it was added has me concerned. The nearest node was far away, so the blue hose was run 150' from a control cabinet to the DHRIO card, and then 150' back where it was spliced with wire nuts. I don't like this setup, but the PLC-5 seems to be OK with it. The DHRIO card will flash red for CH. A, indicating adapter fault, according to the manual, but none of the adapters are faulted. Every PLC-5 chassis was power-cycled after switching to the DHRIO card, yet the DHRIO CH. A flashes red. Occasionally, we saw it say CHAT LINK under CH. A, which I read means "babble" on the RIO network. I couldn't get any further info about this. Two Rockwell techs had no idea what this could be. DHRIO card is brand new.
We had to revert to the PLC-5 so the plant could run, but we'll need some options before we attempt this again.
BEFORE:
PLC-5 Rack 0/1 <> Rack 2/3 <> Rack 4/5 <> Rack 6/7 <> Rack 10/11
AFTER:
Rack 0/1 <> Rack 2/3 <150' blue hose> DHRIO module <150' blue hose> Rack 4/5 <> Rack 6/7 <> Rack 10/11
We had to revert to the PLC-5 so the plant could run, but we'll need some options before we attempt this again.
BEFORE:
PLC-5 Rack 0/1 <> Rack 2/3 <> Rack 4/5 <> Rack 6/7 <> Rack 10/11
AFTER:
Rack 0/1 <> Rack 2/3 <150' blue hose> DHRIO module <150' blue hose> Rack 4/5 <> Rack 6/7 <> Rack 10/11
Last edited: