Hi guys
My mind has gone blank , im using rslogix 500 on a slc 505, I have a existing program which has a oil pump being enigized by a contactor controlled via the plc, I would like to have a timer for duration of the pump running and a timer for the intervals ( frequency ) but my mind has gone blank , can someone point me in the right direction please thanks
 
Use RTO (retentive) timer for the on time and the off time
they retain the accumulated value when the rung is false then continue from thee when true
you just have to reset them at some point
 
the control logic to turn on the pump contactor has 2 functions.
#1 - turn on the pump contactor
#2 start a motor on timer (timer 1)

when timer 1 is done, turn off the oil pump contactor
timer 1 done and oil pump off, start timer 2

timer 2 done resets timer 1

the cycle starts over.

this was done in my head, so you may need to tweek it a bit.

regards,
james.
 

Similar Topics

I have a network with 4 PLCs PLC1 is controllogix and PLCs 2-4 are compactlogix and they all need to communicate. The current way I have this...
Replies
8
Views
260
So to start off: I have no experience with PLC's, but I'm good at figuring stuff out, but I need some help to know if my PLC is just dead in the...
Replies
2
Views
114
Hi guys, I have no experience when working with AllenBradley PLC, but I hope someone could clarify the result of multiplication shown in the...
Replies
14
Views
2,193
To quickly test a plc output which is wired to a relay do I dob a cable between the output and 24vdc+ source I.e something with 24vdc+ live such...
Replies
6
Views
692
Back
Top Bottom