Ml1400
ceilingwalker
Mar 2010
Phoenix, AZ
1,586
Hello all. I went to a customer a couple weeks ago, edited a project in one of their ML1400's. I get a call that the "old alarms are back on the HMI". I go back, upload what is in the CPU and it is a match with the original project I edited! I don't believe anyone there was able to take the old project and reload it so I am suspecting the PLC somehow reloaded the project from elsewhere, maybe? Anyone else have this happen? Thank you
Look at Controller -> Processor Status -> Mem Module in the Controller window of the program. Is the Memory Module Loaded on Boot S:5/8 bit or any other such bits set to 1?
If there's no memory module installed in the controller, then the only possible answer is that somebody onsite downloaded the original program.
No, it is set to "0". Someone must have loaded it locally then, correct?
Saving the project to eeprom is a separate operation. In the rslogix 500 menu click Comms then EEPROM, then store to eeprom. You will have to put the CPU into program mode to do this
Hello, I am new here and have been working with PLCs for a few years now. I have been tasked with setting up a Micrologix 1400….. to a Cmore 10...
489
Hi, We may of finally received out first v21 ML1400. IP address set, proceed to download standard file for our machines & at about the 80% mark...
1,441
I have a Allen Bradely 1500 that has a cracked board. It still works but needs replaced (battery is no longer connected). To make migration easier...
3,223
Hi, I've got a new project for a vacuum conveying system. We require to add another HMI to the existing system which will then feed 2 separate...
1,828
Hi All I have connected a Keyence SR1000 to a Compact Logix PLC and am triggering the scanner and reading barcodes over Ethernet/IP, no issues...
837