Contrologix 1756-IF16 analog input card

jtashaffer

Member
Join Date
Aug 2009
Location
KY
Posts
415
I have a controllogix Plc with a 1756-IF16 analog input card. There are 8 input cables and they only have 2 wires. Then there is a jumper over to the other terminal I think it is rtn. I have to add 3 more analog inputs. Do I need to get another analog input card for this type setup
 
If each cable is connected to 2 input points (example: IN-0 & IN-1), then the module is setup for differential inputs and you therefore don't have a spare channel available. It sounds as though your module is wired for 8 differential current inputs, based upon your description of a jumper to the RTN terminals.

Have you checked to make sure that all 8 cables are actually connected to field devices, rather than merely to a control panel terminal board?
 
They are all being used. Those 8 are for a different type setup. I have to add 3 analog inputs for scales. 1 analog input for each scale. Do I wire it up in the same way?
 
They are all being used. Those 8 are for a different type setup. I have to add 3 analog inputs for scales. 1 analog input for each scale. Do I wire it up in the same way?


You could use single ended inputs for most instruments. You only need to set an analog input module up for differential inputs when your instrument outputs a signal that crosses from negative to positive.

Assuming that your scales have a 4 to 20 mA output, which is typical, then you could use a 1756-IF16 module to facilitate 16 inputs.

The wiring diagrams for that module are shown in this PDF document.
 

Similar Topics

Attempting to update 1756-L55 v10 to v16 through the RSLogix Firmware update utility. On the update firmware progress screen there is nothing...
Replies
0
Views
4,219
I need help with comm issue. I'm trying to communicate from a new Cmore Touchpanel (Automation Direct) using tag-based ethernet comm direct from...
Replies
3
Views
1,908
Hell everyone, Just let me start out by saying i have searched the site but cant find an answer to what i did wrong. I needed to change the IP...
Replies
9
Views
2,450
The title sums up the control system setup. L63 processors with 1756-EN2T for Ethernet I/O which includes over 150 Control Techniques drives...
Replies
4
Views
4,220
Can anyone confirm that using contrologix 5580 controller is not possible to work with powerflex 527? It's been a couple of days now that i am...
Replies
8
Views
1,186
Back
Top Bottom