Help with spec sheet ??
My friends,
I would like your suggestions here. I am developing a spec sheet to be filled out by the sales / mechanical dept. The purpose is to get me the information I need to properly design the control system. We are an OEM building machinery for several industries, including material handling, bulk materials, brick handling, sawing equipment etc. Almost always standard 480V 60hz machines with PLC control and at least one touch screen hmi. Safety systems including zone control. What would you want on such a spec sheet ? Plant Voltage? Environment ? Temperature ? Hazardous location Y/N ? Type of hazard ? Name some items you would want to know before beginning ?
__________________
"Forgiveness is easier to obtain than Permission"! ![]() MATT |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Jun 2008
Location: New York
Posts: 1,390
|
Regulatory and AHJ requirements outside of normal compliance requirements. (IE, for example compliance with CFR 21 Part 11 for Pharma industries)
Safety requirements Ergonomic Requirements Language Requirements |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Oct 2007
Location: Tennessee
Posts: 2,316
|
Since you are the oem, your customer is to provide you with the specs.
questions I would ask. what is the machine and what does it do what is the poser requirements what is the preferred plc and hmi what plc software does the company have what is the environment that the equipment is to be located !!! Details up front is time consuming, BUT will save your rear end in the long run! the more you ask, the more you know and learn, the more the price stays the same or goes up. we always spell out what we are providing in detail. if we get the job and quote is as a regular environment and the customer fails to tell us its a classified area, we have our quote we sent to them to fall back on. lots of other questions, but this is a start. james |
![]() |
![]() |
#4 | |
Member
|
Quote:
Thank You ! This is the type of info I am looking for. I seem to get bitten on the rear end with every project because of this lack of communications...
__________________
"Forgiveness is easier to obtain than Permission"! ![]() MATT |
|
![]() |
![]() |
#5 |
Lifetime Supporting Member
|
HMI requirements - color, screen size, etc.
Selector switches, pilot lights, pushbuttons, manual override requirements Communications requirements for SCADA, protocols, etc. Customer preferred PLC brand Field instruments to be provided and powered |
![]() |
![]() |
#6 | |
Member
|
Quote:
Great Choices !!
__________________
"Forgiveness is easier to obtain than Permission"! ![]() MATT |
|
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Oct 2007
Location: Tennessee
Posts: 2,316
|
I would also ad what type of plc programming to use an what to exclude.
we use ladder logic only. we do not allow fuzzy logic, grafcet, structured text, function blocks, sequencers, fifo. ladder logic only and have the program given to maintenance to look at first. the reason is that most maintenance personnel understand basic ladder logic. james |
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Nov 2016
Location: Fields of corn
Posts: 1,215
|
I doubt that most companies would contact you and not give this, but I would nevertheless ask about their HMI and PLC programming standards.
|
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Oct 2007
Location: Tennessee
Posts: 2,316
|
Specify the brand names and model #'s for the plc with spare requirements, hmi brand, scada brand and tag size with spares.
Specify everything !, or you may be forced to accept what they give you which can turn out to be a boat anchor. SPECIFY that all cylinders have sensors at each end for example. running a bunch of cylinders using timers is a total waste of time! load cells are to be rated for impact shock which means a that a 25 lb load cell must be rated for 250 lbs due to shock or they will only last for a month or 2, then they wear out. string pots must have mechanical support such that the end of the pot does not bend ad the connection point and break due to fatigue. james |
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Jun 2017
Location: Michigan
Posts: 85
|
It depends on what type of controls you deal with often. For me the first questions I have to ask here are:
Is the machine indoors or outdoors? Desired \ Required panel rating? (NEMA 4, 4x, 12, etc) Does this have to be UL certified? Control voltage: 24VDC or 120VAC? How many motors, what HP rating for each, and VFD or Contactor control? Local \ Remote modes required for each motor? Are we using a PLC\HMI? (Yes, unfortunately, I still design relay panels every now and then) PLC Brand \ Series HMI Brand \ Series Communications protocol Interlocks (with Plant via ethernet \ dry contacts \ connector \ etc) Based on that information alone, I have a pretty good idea of panel size and cost. I'll also ask for them to either give me a sequence of operations (or at least how they think it should run) or I'll take the information above and write my own sequence to give to them. Sequences written out is a really easy way to communicate with people who don't understand controls (ie - almost all project managers) |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Mitsubishi MX Sheet Excel addon | doomsword | LIVE PLC Questions And Answers | 6 | February 7th, 2017 12:00 PM |
FactoryTalk SE alarm history data logging to separate Excel Sheet | minaykha | LIVE PLC Questions And Answers | 1 | April 29th, 2016 07:53 AM |
RSLogix 5000 FB sheet size | russrmartin | LIVE PLC Questions And Answers | 4 | June 15th, 2006 11:37 AM |
sheet edge detectors | ldavis7999 | LIVE PLC Questions And Answers | 8 | November 9th, 2003 01:24 AM |
opensource PLC projects in C... | s_viswesh | LIVE PLC Questions And Answers | 13 | October 17th, 2002 05:39 PM |