#16 |
Member
|
If you go online w/ the plc, doesn't it show the fault type?
|
![]() |
![]() |
#17 |
Member
![]() ![]() Join Date: Mar 2018
Location: Minnesota
Posts: 11
|
It does not. Nor does it show it as being faulted in the dropdown menu where you can see "Remote Run", "Go Offline", etc. All of the Status Error bits are clear as well.
|
![]() |
![]() |
#18 |
Lifetime Supporting Member + Moderator
|
Have you deleted the Harmony files?
If you have not see these tech notes https://rockwellautomation.custhelp....il/a_id/769010 and https://rockwellautomation.custhelp....tail/a_id/5765
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways Last edited by geniusintraining; October 11th, 2018 at 02:29 PM. |
![]() |
![]() |
#19 |
Member
![]() ![]() Join Date: Mar 2018
Location: Minnesota
Posts: 11
|
I can't do that myself without Admin access on the computer. IT at corporate are the only ones who have that access and I have requested that they remote in and do this. So far they have not yet.
|
![]() |
![]() |
#20 |
Member
![]() ![]() Join Date: Jun 2018
Location: Plainfield IN
Posts: 355
|
Yup IT can be a pain 8 years ago I got tired of waiting for our IT to come and do there job I used http://ophcrack.sourceforge.net/ to get the passwords and used the admin when I needed to do something my self instead of waiting days for them. Then I finally talked them into giving me admin rights.
YAAY for me? |
![]() |
![]() |
#21 |
Member
|
If I had to work at a company w/ an IT department, I would def. run everything off of a virtual box.
|
![]() |
![]() |
#22 |
Lifetime Supporting Member + Moderator
|
I noticed something yesterday on RSLinx
Using the Ethernet devices driver a SLC 5/05 1747-L552 C/8 DC 2.59 says its faulted. Looking at the same device using Eth I/P driver says its OK. A similar device next to it, a SLC 5/05 1747-L551/C C/11 DC 3.46, does not do the same thing. Its fine on both ETH and ETH I/P . And both machines are working just fine. Looks that way right this minute in fact. |
![]() |
![]() |
#23 |
Lifetime Supporting Member
![]() ![]() Join Date: Oct 2013
Location: Aalborg
Posts: 100
|
My Money is on an error in RSLINX, do your colleges get the same error when going online from a different PC ?
It is rare that RSLINX is working perfect, (don't want to calculate the hours wasted) |
![]() |
![]() |
#24 |
Lifetime Supporting Member + Moderator
|
I have no colleagues... sniff.
But I agree with you about Linx |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
SLC 5/05 controlling Powerflex 525 drives over Ethernet ??? | sparky mark 9876 | LIVE PLC Questions And Answers | 6 | November 30th, 2016 01:45 PM |
SLC 5/05 Ethernet Communications | Tharon | LIVE PLC Questions And Answers | 13 | September 4th, 2015 02:17 PM |
SLC 5/05 to Field Server PCCC? Explicit? | Phillyblunz | LIVE PLC Questions And Answers | 11 | August 5th, 2014 05:12 PM |
SLC 500 Ethernet Setup | JSPLC | LIVE PLC Questions And Answers | 3 | June 1st, 2010 05:15 PM |
help with SLC 5/05 | tafenegus | LIVE PLC Questions And Answers | 2 | September 16th, 2008 09:47 AM |