5069 I/O fault

I added a 5069-OW16 module to a system yesterday that currently has a 5069-L306ER processor and a 5069-IY4 module. The OW16 was tested and running when I left yesterday, but I got a call this morning saying that the pump we wired to it was not running and the card's MODULE STATUS indicator was flashing red. What could possibly make that card fault while the rest of the system is running OK?
  Reply With Quote
Old October 11th, 2018, 07:15 AM   #2
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SouthEast Michigan
Posts: 3,272
Module configuration will dictate if a controller controller fautl occurs if the connection fails while in Run Mode. See the Connection Properties of the module and the setting "Major Fault On Controller If Connection Fails While In Run Mode".

As far as why the module faulted, I don't have that magic sense that can reach out to the circuit and tell you why; wish I did.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old October 11th, 2018, 08:18 AM   #3
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 774
Quote:
Originally Posted by jstolaruk View Post
Module configuration will dictate if a controller controller fautl occurs if the connection fails while in Run Mode. See the Connection Properties of the module and the setting "Major Fault On Controller If Connection Fails While In Run Mode".

As far as why the module faulted, I don't have that magic sense that can reach out to the circuit and tell you why; wish I did.
I'm just wondering what things can make a module fault like that. I've never seen it happen. Brand new out of the box module, too.
  Reply With Quote
Old October 11th, 2018, 11:27 AM   #4
tarik1978
Member
Morocco

tarik1978 is offline
 
Join Date: Mar 2010
Location: casablanca
Posts: 396
Is the power on 5069-OW16 24VDC or 120VAC?

5069-OW16 Channel Status LEDs are flashing red after applying 120 VAC SA Power
1070979 | Date Created: 12/14/2017 | Last Updated: 02/09/2018
Access Level: Everyone
https://rockwellautomation.custhelp....l/a_id/1070979
  Reply With Quote
Old October 11th, 2018, 11:41 AM   #5
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 774
Quote:
Originally Posted by tarik1978 View Post
Is the power on 5069-OW16 24VDC or 120VAC?

5069-OW16 Channel Status LEDs are flashing red after applying 120 VAC SA Power
1070979 | Date Created: 12/14/2017 | Last Updated: 02/09/2018
Access Level: Everyone
https://rockwellautomation.custhelp....l/a_id/1070979
The module is on 24VDC power. As I stated, the MODULE STATUS is flashing red, not the channel status.

Supposedly with these new 5069 relay output modules, they don't have any internal suppression for inductive loads (which I would guess account for the majority of loads out there), so connecting an inductive load, as we did, to power a motor starter, can introduce "noise" into the module and cause it to fault. Talk about poor design. Funny how the 5069-OW16 manual makes no mention of this and it took a call to AB tech support to reference a Tech Note about such loads. Not impressed.

Last edited by phuz; October 11th, 2018 at 11:45 AM.
  Reply With Quote
Old October 15th, 2018, 04:44 PM   #6
hugobear
Member
United States

hugobear is offline
 
Join Date: Aug 2015
Location: STP, MN
Posts: 3
same problem happening here

I am troubleshooting a rack of 5069 I/O that has been experiencing repeated comms failures as well. I have 1 5069-OW16 in the rack, connected to a half-dozen or so old 24VDC MAC valves. The first time I saw this error it was this card at the main point of failure (all cards to the left were still talking). But since then it seems to be the entire rack going off-comms when it happens. All I/O is 24VDC, no 120VAC. The rack config is below:

5069-L310ERS2
5069-IB16
5069-IB16
5069-OB16
5069-FPD
5069-OW16
5069-HSC2xOW4
5069-IB16
5069-IB16
5069-IB16

Anyone have any luck fixing/working around this problem?
  Reply With Quote
Old October 15th, 2018, 04:55 PM   #7
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 774
Quote:
Originally Posted by hugobear View Post
I am troubleshooting a rack of 5069 I/O that has been experiencing repeated comms failures as well. I have 1 5069-OW16 in the rack, connected to a half-dozen or so old 24VDC MAC valves. The first time I saw this error it was this card at the main point of failure (all cards to the left were still talking). But since then it seems to be the entire rack going off-comms when it happens. All I/O is 24VDC, no 120VAC. The rack config is below:

5069-L310ERS2
5069-IB16
5069-IB16
5069-OB16
5069-FPD
5069-OW16
5069-HSC2xOW4
5069-IB16
5069-IB16
5069-IB16

Anyone have any luck fixing/working around this problem?
Unfortunately, it looks as if you need to use a load resistor. Because we did not have one, and needed to keep running, I had the electricians wire in a temporary 24vdc ice-cube relay to drive the starter. We are upgrading the starter very shortly and I strongly suggested a 24vdc coil. So far it's been OK on 24vdc. Still not happy with the results.

I notice you have an FPD in your tree. Why is that? Extra power?
  Reply With Quote
Old October 15th, 2018, 10:38 PM   #8
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SouthEast Michigan
Posts: 3,272
I found in the last 5069 commission that the inut modules are very sensitive to noise on the input signal wires; more so than 1769 or 1734 inputs. Extra care had to be taken to route wiring father away from vfd output wiring than in the past.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old October 16th, 2018, 10:38 AM   #9
hugobear
Member
United States

hugobear is offline
 
Join Date: Aug 2015
Location: STP, MN
Posts: 3
Quote:
Originally Posted by phuz View Post
Unfortunately, it looks as if you need to use a load resistor. Because we did not have one, and needed to keep running, I had the electricians wire in a temporary 24vdc ice-cube relay to drive the starter. We are upgrading the starter very shortly and I strongly suggested a 24vdc coil. So far it's been OK on 24vdc. Still not happy with the results.

I notice you have an FPD in your tree. Why is that? Extra power?
The FPD was (I'm told) a result of the design in IAB. The engineer designing this followed the IAB guidelines and I thought doing that would pose no problems. The IO in the cabinet is all 24v, no 120v anywhere in the box. All the VFDs are in a separate cabinet but the inputs and VFD cables may be too close somewhere on the machine. That said... I'm VERY disappointed that it's that finicky on noise. If this were all 1756 IO I'd be virtually certain this wouldn't be happening.
  Reply With Quote
Old October 16th, 2018, 10:44 AM   #10
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 774
Quote:
Originally Posted by hugobear View Post
The FPD was (I'm told) a result of the design in IAB. The engineer designing this followed the IAB guidelines and I thought doing that would pose no problems. The IO in the cabinet is all 24v, no 120v anywhere in the box. All the VFDs are in a separate cabinet but the inputs and VFD cables may be too close somewhere on the machine. That said... I'm VERY disappointed that it's that finicky on noise. If this were all 1756 IO I'd be virtually certain this wouldn't be happening.
You're correct. This doesn't happen with 1756 I/O. I have several of these 5069 PLCs installed at various customers and I'm wondering if it was a bad choice.
  Reply With Quote
Old October 16th, 2018, 10:57 AM   #11
hugobear
Member
United States

hugobear is offline
 
Join Date: Aug 2015
Location: STP, MN
Posts: 3
Quote:
Originally Posted by phuz View Post
You're correct. This doesn't happen with 1756 I/O. I have several of these 5069 PLCs installed at various customers and I'm wondering if it was a bad choice.
We're in the same boat... went with the new platform for the longest life cycle available and now we have random IO failures. Not good...
  Reply With Quote
Old October 16th, 2018, 10:57 AM   #12
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SouthEast Michigan
Posts: 3,272
I use the FPD to isolate motion and non-motion output power; typically the FPD is powered when safe conditions exist (safety relay).
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old November 22nd, 2018, 09:28 AM   #13
rickhughes
Member
Canada

rickhughes is offline
 
Join Date: Jul 2008
Location: mississauga
Posts: 2
I have the same issue on 2 installs. 5069-IQ16 24vdc input at reference does not initiate the input. Re-routing of the wiring solved the issue. 5069-IF8 input properly shielded had to be re-routed not to induce a fault on the card.

I have discontinued using the 5069 i/o until AB solves the issue.

Rick
  Reply With Quote
Old November 22nd, 2018, 09:57 AM   #14
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 774
Quote:
Originally Posted by rickhughes View Post
I have the same issue on 2 installs. 5069-IQ16 24vdc input at reference does not initiate the input. Re-routing of the wiring solved the issue. 5069-IF8 input properly shielded had to be re-routed not to induce a fault on the card.

I have discontinued using the 5069 i/o until AB solves the issue.

Rick
Have you made AB or your supplier aware of this? If we want a fix, it's important that they know of all these issues.
  Reply With Quote
Old November 24th, 2018, 03:40 PM   #15
rickhughes
Member
Canada

rickhughes is offline
 
Join Date: Jul 2008
Location: mississauga
Posts: 2
Of course I informed my AB rep of the issues, and I apologized for wasting his time after he deduced that I must have incorrectly applied his product (for the past 40 years).

Rick
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Point I/O vs Flex I/O Ih8Siemens LIVE PLC Questions And Answers 14 March 12th, 2018 07:01 AM
L35E repeated major fault rainagain LIVE PLC Questions And Answers 5 October 10th, 2017 06:59 AM
Compact I/O vs Point I/O ASF LIVE PLC Questions And Answers 13 September 29th, 2015 01:38 AM
Controllogix elledge LIVE PLC Questions And Answers 43 February 12th, 2014 03:55 AM
Point I/O fault Hydro Power Guy LIVE PLC Questions And Answers 0 August 22nd, 2012 08:41 AM


All times are GMT -5. The time now is 02:17 AM.


.