I just start learning PLC , so belows the question I hope there will be someone to explain to me:


after reading the One Shot of the PLC on-line learning, I am very confused with
the "DIFU" instruction! I am not very clear about the function of the DIFU
instruction! Could you explain to me by email?

Looking forward to seeing your reply!
 
Sorry, but I don't think I can do a better job explaining it than Phil has already done. Have you watched the animation?

If you still need help, try to be more specific about what part you don't understand...

-Eric
 
On second thought....

Hold on a minute! I just looked at Phil's tutorial and I can see where it might be confusing...

The DIFU instruction is an OUTPUT, though it is shown midway across the rung!

For the first rung, try using this (with Phil's explanation):



0000 +-------+
|----] [--------------| DIFU |
| |
| 1000 |
+-------+




Does that help any?

-Eric
 
Think of the DIFU as an output coil. It can operate as many contacts as necessary in your program. The difference is that, unlike the iniating contact, the contacts of the DIFU are only on for the length of one PLC scan. :nodi:
 
Sometimes "terminology" gets in the way of understanding an idea.

The basic concept here is, "Tell me when...

"Bit-X just went ON" -OR- "Bit-X just went OFF"

We are looking for the "transition" from OFF-to-ON -OR- ON-to-OFF.

On any given scan, the bit is either ON or OFF. Now, compare that state to the previous state. If the current and previous states are the same, then there has not been a transition and therefore, no need to indicate that a transition has occurred.

If, on the other hand, the current state is different from the previous state, then a transition has occurred and, therefore, (if you are watching for such things) there is a need to indicate that the transition has occurred.

At that point, it would be nice to know if the transition was from OFF-to-ON or ON-to-OFF.

If there was a transition and the current state is ON, then the transition was from OFF-to-ON.

If there was a transition and the current state is OFF, then the transition was from ON-to-OFF.

On the next scan, the PLC again compares the current state to the previous. If the current state is the same as the previous, then there has been no transition since the last scan and so the "transition-flag-bit" turns OFF. Thus, the particular bit is ON for only 1 scan.

Having this capability allows you to respond when an event happens to a particular bit rather then the state of that particular bit.

Some PLC's use...

--|/\|-- to look for OFF-to-ON

--|\/|-- to look for ON-to-OFF
 
As usual, Terry has the inate capability to make complex subjects simple. With your permission, I would like to use your description of one shot in my training courses.
Check's in the mail. uragod
 

Similar Topics

and then when i open the windowmaker, intouch is shutdown... that's not work that's demo I have 30days demo
Replies
3
Views
159
Hi All In my plc program in following picture there are functions FC50 in the begining and FC51 in end of organization block OB32. I can not...
Replies
3
Views
965
Just for readers in the US, when I write 'gas' I mean it as a state of matter, not shorthand for gasoline :-) I don't understand the logic of a...
Replies
39
Views
11,162
Hello all, I have recently been working on a project utilizing Allen Bradley PLC/HMI. It's an L16ER-BB1B PLC and a Panelview Plus 7 HMI. I'm...
Replies
15
Views
5,666
I’m using rslogix5000 v20 with ControlLogix L72. I added some rungs to monitor time meter of our propulsors. But with same ladder instruction I...
Replies
11
Views
4,012
Back
Top Bottom