1747sn to 1794 flexio 32bit config problems

MicB

Member
Join Date
Aug 2005
Location
Taupo
Posts
9
Hi,
I am trying to get some flexi IO communicating.
The scanner has its steady green light on The G file is all the default values.The first two green lights are working on the 1794 module. So I think they are communicating to each other.
In the 1794 module all S1 switches are on
s2-3 and s2-4 are off all the rest are on
I have a 32 input module and a 32output module connected to the 1794.respectively
I am using a basic BTR trying to get data from the 1794
The BTR is setup as follows
Rack 0
Group 0
slot 0
control block N7:10
Data file n7:20
Buffer M1:1:100
Req word count 1
Transmitted
control block lenght 3

When I set the rung true after approx 4 secs I get -9 in the transmitted line.

After we sort out this basic problem if I cahngwe req word count to 2 will that return inputs 0 -32?

Thanks
Mike
 
With Flex I/O, the meaning of some of the dipswitches has been changed by A/B more than once. Be very sure your dipswitch settings are correct for the exact revision of your 1794-ASB.
 

Similar Topics

J
I am having trouble with an existing SLC5/05. It was working fine but after power cycle, we lost data to all but 1 1794-IE8 module. I looked at...
Replies
4
Views
3,112
Does anyone know of an AB publication for RIO BTW/BTR to the 1794IE8, The only literature I find on AB site is PLC-3 & PLC-5 I am using 1747SN, I...
Replies
3
Views
13,540
The problem started with an error 208 in my PV900 after a program change and download to my slc 5/04. The logic had worked for over 2 years...
Replies
2
Views
2,766
Hi currently my work parther an I are working into trying to visualize a set of values on a PanelView 550 that is connected tru a RIO connection...
Replies
15
Views
6,502
Hey Everyone, After reading a lot on this forum and elsewhere I see not many are fond of the 1794-VHSC module. I can see to a degree as I was...
Replies
3
Views
152
Back
Top Bottom