Anyone have any luck making an AOI that checks the comms status of an Ethernet device? I have an AOI for VFD control that I use, and I always have to make a separate section of code to check if the drive is online, usually using a GSV instruction pointed to the module itself.

I'm playing around with putting the GSV instruction in the VFD AOI directly, but it seems that the name of the VFD itself needs to be of the data type of the VFD created by the AOP- "AB:powerFlex525V_EENET_Drive:I:0" for me, while the GSV value needs to be of the type "Module." So this forces the user have to have two inputs into the AOI for the same VFD tag, essentially.

I was curious if anyone else has tried this and if they were able to figure out a better solution.
 
Anyone have any luck making an AOI that checks the comms status of an Ethernet device? I have an AOI for VFD control that I use, and I always have to make a separate section of code to check if the drive is online, usually using a GSV instruction pointed to the module itself.

I'm playing around with putting the GSV instruction in the VFD AOI directly, but it seems that the name of the VFD itself needs to be of the data type of the VFD created by the AOP- "AB:powerFlex525V_EENET_Drive:I:0" for me, while the GSV value needs to be of the type "Module." So this forces the user have to have two inputs into the AOI for the same VFD tag, essentially.

I was curious if anyone else has tried this and if they were able to figure out a better solution.

Hi Rupej.

Yes this has been discussed before; in summary if you are using v24+ then you can pass the data type 'MODULE' directly into your AOI (thus doing everything). If you are using anything less than v24 then unfortunatley you do have to complete the GSV outside hen pass in the entry status.

I do have the 2 versions of AOI...I will upload next time im at my computer.

http://www.plctalk.net/qanda/showthread.php?t=118476

Regards

Daniel.
 
Last edited:
Thanks Daniel, that's a helpful link. I'd also love to see your examples when you get a minute.

I've been able to use the 'MODULE' data type to get the GSV instruction to work, but I haven't been able to use it to extract drive parameters. For example, if I try to include a (Name of Module Parameter):I.Ready bit in my logic, I get an error that the referenced tag is undefined.
 

Similar Topics

Hi. I'll say it again, I worked mostly with Unity Pro for the last 12 years and I'm trying to convert our FBD standard to Rockwell Logix...
Replies
13
Views
1,484
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
Replies
3
Views
100
Does anyone know how to set the background colors of instuction blocks (TON, MOV, etc)?
Replies
1
Views
107
Hello all, I'm trying to use the Logix Designer SDK to upload and download a single ACD to many controllers. I got this to work fine copying...
Replies
0
Views
56
Hello, I am trying to connect a Stride Analog Output module to a 1769 CompactLogix via Ethernet. I added a new Generic Ethernet Module for the...
Replies
4
Views
198
Back
Top Bottom