The setpoint should be compared to the EU range, which in this case is incorrectly configured. The PID block scales the input PV (0-4095) to Engineering Units, and then calculates the error from Set Point. (Also in EU). The print outs show EU of 0-4095, it should be what ever the input scaling is (assume Type J) then 32-1400F.
__________________
Certified Siemens Functional Safety Professional,
ID: SFSP17010238
https://azr.com/
  Reply With Quote
Old April 8th, 2021, 02:33 PM   #32
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,868
Quote:
Originally Posted by drbitboy View Post
The bang-bang behavior suggests otherwise, and it depends on how the output is scaled, but with the PV range set to [0-4095] and the temperature in degrees, a 1 degree change is 0.025% of full scale, so 50 is not the most outrageous proportional gain.


Or am I still not grokking the scaling of the PD-based PID?
Going to have to wait till I get there to find out what is true settings.
The screen shots I sent of the PID were from 2011... I ASSUME no one else has been in the logic...
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old April 8th, 2021, 02:34 PM   #33
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,868
Quote:
Originally Posted by Ken Moore View Post
The setpoint should be compared to the EU range, which in this case is incorrectly configured. The PID block scales the input PV (0-4095) to Engineering Units, and then calculates the error from Set Point. (Also in EU). The print outs show EU of 0-4095, it should be what ever the input scaling is (assume Type J) then 32-1400F.
Type K is control...
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PID control (PLC5) jeffblichmann LIVE PLC Questions And Answers 4 October 9th, 2012 01:36 PM
RSlogix PLC5 PID help! DeweyfromOhio LIVE PLC Questions And Answers 13 July 9th, 2012 07:50 PM
PLC5 PID triggering curiosity - confirm my thougths please wildswing LIVE PLC Questions And Answers 2 November 22nd, 2011 11:48 AM
ControlLogix general + PID "best practices" wildswing LIVE PLC Questions And Answers 6 October 10th, 2011 11:37 AM
PID output scaling PLC5 russrmartin LIVE PLC Questions And Answers 2 January 30th, 2004 05:45 PM


All times are GMT -4. The time now is 07:07 PM.


.