Help Needed, Siemens 300 To Mitsi HMI
I have a siemens 317-2 and an old GOT1000 (GT1675M - V)
I am trying to get the darn things communication and having no luck. I have followed the guides online and still no good. I have them both connected via ethernet. Does anyone have a guide / project or knows what settings I need to change to get it to work. Thank You All |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
I dont know Mitsubishi.
But a common mistake for any HMI connecting to a Siemens S7 is to specify the wrong rack/slot combination. For an S7-300, rack must always be 0, and slot must always be 2.
__________________
Jesper ![]() See my profile interests for Q&A
|
![]() |
![]() |
#3 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2015
Location: Yokohama
Posts: 545
|
Which GOT model are you using and which Protocol (serial, Ethernet). please provide a bit more details
|
![]() |
![]() |
#4 |
Member
|
Perhaps look at this post on the Siemens website
https://support.industry.siemens.com...=0&pageSize=10 |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Nov 2016
Location: England
Posts: 78
|
I have the HMI connected to port X2 on the CPU. The Mitsubishi software says i need to enable Fetch and Write in the Siemens but I cant find the option for this.
CPU - 317-2 PN/DP HMI - GOT1000 Model GT1675M - V |
![]() |
![]() |
#6 |
Member
|
Here is another link for coms although it is in german but might have some examples
https://support.industry.siemens.com...dl=en&lc=de-WW |
![]() |
![]() |
#7 |
Lifetime Supporting Member + Moderator
|
It is possible to setup a socalled passive fetch/write connection on the Siemens side.
Maybe that is what they mean ? But as far as I know, fetch/write is only possible with an ethernet CP343-1 module, not with the integrated PN port in the CPU. In the link parky posted, it is described that you only have to specify the IP and an unused port, and it should work. So... I dunno.
__________________
Jesper ![]() See my profile interests for Q&A
|
![]() |
![]() |
#8 |
Lifetime Supporting Member + Moderator
|
The 2nd link by parky cannot be right.
It is about letting the PLC actively send to or fetch data from a partner by the PUT/GET method. I doubt that is what is used with the Mitsubishi panel.
__________________
Jesper ![]() See my profile interests for Q&A
|
![]() |
![]() |
#9 |
Lifetime Supporting Member + Moderator
|
I have found the Mitsubishi manual, and they only refer to that the ethernet connection is possible with a CP343-1. So I think that it is what they mean, that you have to add a CP343-1 to the S7-300 rack, and then setup two ISO_ON_TCP connections on the S7 PLC, and in these connections the mode must be set to Fetch passive and Write passive respectively.
I dont like it, it costs an expensive CP343-1 (a CP343-1 LEAN does not support fetch/write). And fetch/write is an arcaic method that is mostly used with exchanging data with legacy Siemens S5 PLCs.
__________________
Jesper ![]() See my profile interests for Q&A
|
![]() |
![]() |
#10 | |
Member
![]() ![]() Join Date: Nov 2016
Location: England
Posts: 78
|
Quote:
|
|
![]() |
![]() |
#11 |
Lifetime Supporting Member + Moderator
|
For info, I checked if you could use a socalled HMI Adapter (6ES7972-0CA11-0XA0).
Unfortunately it has been discontinued. Only available as spare part. It will be expensive if you can get it.
__________________
Jesper ![]() See my profile interests for Q&A
|
![]() |
![]() |
#12 |
Supporting Member
![]() ![]() Join Date: Jan 2008
Location: Belgrade
Posts: 413
|
I haven't used GOT1000 with S7-300, but I have used it with S7-200 and PPI cable without problems (6ES7 901-3BF20-0XA0 - RS232/PPI). I also have seen working S7-300 with GOT1000. It was 8 bits, 1 stop bit, Odd and you need to have good Host and Adapter address.
|
![]() |
![]() |
#13 |
Lifetime Supporting Member + Moderator
|
I think that maybe this is an alternative to 6ES7972-0CA11-0XA0:
https://www.plccable.com/siemens-plc...solated-cable/ Going via serial/MPI may be just as fast as via a CP343-1, since the data has to pass via the slow MPI backplane anyway. No guarantee that it will work ! But at 80 USD it could be worth a try.
__________________
Jesper ![]() See my profile interests for Q&A
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Connect Siemens HMI 6AV2 124-0MC01-0AX0 with PC/Laptop | akhmadzaki | LIVE PLC Questions And Answers | 1 | January 11th, 2021 03:16 AM |
Siemens hmi profinet question | tommee10533 | LIVE PLC Questions And Answers | 1 | September 10th, 2014 05:08 PM |
Siemens TIA HMI Download Problems | b-stack | LIVE PLC Questions And Answers | 17 | August 7th, 2014 10:19 PM |
Communication Siemens S7 300 X Hitech HMI | KendiSaito | LIVE PLC Questions And Answers | 0 | April 25th, 2012 03:43 PM |
Siemens HMI Advice | dharrington86 | LIVE PLC Questions And Answers | 0 | April 4th, 2012 01:37 PM |