Old March 15th, 2019, 02:12 PM   #1
KingPresident
Member
United States

KingPresident is offline
 
Join Date: Aug 2015
Location: Michigan
Posts: 90
MSG not pushing to buffer dint?

I have 2 configured PLC's that send and receive MSG's.

PLC 1

Set to CIP Data table Read
MSG Source is msgFROMplc2.dint[0]
MSG Dest is InputBuffer.dint[0]



I can send a value from PLC2, AND I can see it show up in PLC 1 at msgFROMplc2.dint[0], but the MSG will not push it to InputBuffer.dint[0]

However, I can use a MOV to move the value from msgFROMplc2.dint[0] to InputBuffer.dint[0] and it works, but I would think that it should be moved by the MSG instruction, not my additional MOV.


Clear as mud?
Is this normal, and if not, what am I doing wrong?

I am enabling and resetting every 1 second.
  Reply With Quote
Old March 15th, 2019, 02:48 PM   #2
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,768
http://www.plctalk.net/qanda/showthread.php?t=117008

The above thread may help you out.
You have not specified the PLC's that you are using.
"The MicroLogix 1400 doesn't know about CompactLogix tag names, so you have to take the extra step of setting up a "PLC/SLC Data Table Map" in the CompactLogix to correlate an INT or REAL[x] array tag to a Data Table address like N7 or F8."

Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
  Reply With Quote
Old March 15th, 2019, 02:56 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,512
Quote:
I can send a value from PLC2
Explain exactly what you mean by "send".

Some old platforms of PLCs required you to set up a Send instruction in one controller and a Receive instruction in another, as a matching pair. Allen-Bradley controllers do not.

A CIP Data Table Read instruction executed in "PLC-1" will request the value of the Source Element (msgFROMPLC2.dint[0]) from the other controller "PLC-2", and place its value in the Destination tag (InputBuffer.dint[0]).

You can choose to use CIP Data Table Read or CIP Data Table Write, as appropriate for your application.

But you only need one instruction for each transfer of data.
  Reply With Quote
Old March 18th, 2019, 11:30 AM   #4
KingPresident
Member
United States

KingPresident is offline
 
Join Date: Aug 2015
Location: Michigan
Posts: 90
Ken, thanks for that.

I was doing it wrong. I had MSG instructions on both plc's referencing the same tag.

Solution: I eliminated the MSG's on PLC2, now all works as intended. /thread.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
adding slc 500 to rs5000 for messaging Rippey574 LIVE PLC Questions And Answers 15 September 12th, 2017 05:24 AM
Multiple MSG instructions SLC5/05 TO SLC5/05 glenncooper LIVE PLC Questions And Answers 7 January 4th, 2017 07:59 AM
Siemens STL Counter TrainS7 LIVE PLC Questions And Answers 8 March 28th, 2016 01:21 PM
1769-SM2 Modbus RTU - MSG Command Freezing calvin127 LIVE PLC Questions And Answers 0 January 22nd, 2014 08:25 PM
Another SLC MSG problem Russff LIVE PLC Questions And Answers 3 March 22nd, 2006 03:25 PM


All times are GMT -5. The time now is 02:11 PM.


.