How to tell if a Motor is really running?

Bullzi

Lifetime Supporting Member
Join Date
Jun 2012
Location
Colorado
Posts
1,530
Hi Everyone,
I have a Fan that recently did not start running when it was suppose to. The PLC is monitoring the Contactor AUX contact to get its run status. The AUX must have been pulled in but for some reason the fan motor did not run. If the AUX did not pull in the system would have shut down on alarm but that didn't happen. The system was running normally but the fan was not running. The main breaker to the fan motor is also feeds the CVT for the panel so I know that was on or the system would have not ran at all.

This is a situation where I need the fan to be running for the equipment to operate safely. So I am looking for ideas on how to know the motor is running other than using the AUX contact. I was thinking of using a current switch on the wires to the motor. Anyone have experience with those?

Any ideas you have would be very helpful.
Thanks!
 
Without any 'smart' devices involved, I'd address the intended purpose of using the motor.

In your particular case, a fan, I'd use a simple air flow switch (paddle style); this will also ensure feedback for a catastrophic fan prop or drive belts failure when the motor is still running, however without moving any air.
 
Last edited:
Flow switch to prove flow and/or a current switch. I've used both, current switch is easier to field install especially if your controls are in the same panel as the motor contactor since you would not need to install any conduit. Best to get one that has adjustable trip point and adjust it so that if the fan belt breaks the current will drop low enough to turn off the switch even with the motor running. Obviously both the current and flow proof would be better than just one.
 
Without any 'smart' devices involved, I'd address the intended purpose of using the motor.

In your particular case, a fan, I'd use a simple air flow switch (paddle style); this will also ensure feedback for a catastrophic fan prop failure when the motor is still running, however without moving any air.

Agreed. If the fan being in motion is an important part of the safety of the process, you'll want to measure fan motion, not any form of measuring the motor alone. Depending on how fast the fan moves, you could also use a photosensor or some other type of prox that could detect the motion of the fins themselves. But I think the air flow switch would be the best choice.
 
Last edited:
Monitor the load (current draw) on the motor and airflow. The airflow will provide the best info as to the fan actually running but the current draw is also good info to have to help predict failures and/or maintenance needs.
 
Cheapest and easiest would likely be an analog current measurement. You can do the wiring in the starter, and it should not be a big cable run to your PLC.

Motor amps should be around 1/3 full load amps for just turning without load. Depending on what current you draw with the fan load, if you drop down under 1/2 you can alarm that the fan is not actually turning.

The air switch flow would be best, but it is a bit more money and takes some wiring to bring the signal back.

I hate switches - they are difficult to calibrate and can fail off or fail on. 4 -20 mA signals are what I use when I have the choice.

If this is a safety application, it's not really much more money for the analog signals compared to hurting someone, or having your plant fill with smoke!
 
Flow switch to prove flow and/or a current switch. I've used both, current switch is easier to field install especially if your controls are in the same panel as the motor contactor since you would not need to install any conduit. Best to get one that has adjustable trip point and adjust it so that if the fan belt breaks the current will drop low enough to turn off the switch even with the motor running. Obviously both the current and flow proof would be better than just one.


The only problem I see with inferring air flow due to normal current draw is that a mechanical issue (such as a failing bearing) could be restricting airflow without dropping the fan amps.
 
The only problem I see with inferring air flow due to normal current draw is that a mechanical issue (such as a failing bearing) could be restricting airflow without dropping the fan amps.

That is true. Measuring the airflow (proof or actual flow measurement) is best.
 
The only problem I see with inferring air flow due to normal current draw is that a mechanical issue (such as a failing bearing) could be restricting airflow without dropping the fan amps.

Thats why we used all three in one of our processes, it was critical to maintaining LEL due to the highly flammable fumes that we were trying to evacuate from the area, its a nightmare from the maintenance standpoint... and then you would have the off shift jumpering everything because they are to lazy to climb stairs and check it out
 
......But I think the air flow switch would be the best choice.


I agree, air flow is the prime object for measurement. The fan may be running, but some ducting blocked somewhere could mean it's not producing air flow.
 
Change to using a solid state overload relay that can give you an actual motor current signal back to your PLC. So instead of just monitoring the six contact, you look for a minimum amount of current to flow. Base that minimum value on the fan current when sufficient air is flowing, which will mean any dampers etc are opennas well (dampers closed = no flow = lowest load on the motor). This tells you what you need to know.
 
Current Sensor (4-20ma output) $25.00. This would even show you if belts broke, because the current will be a different value when things are working correct and not correct.
 

Similar Topics

sir plz tell me how to interface servo motor with abb micrologoc 1400b plc plz give me detail of instruction and wht type driver may i use or tell...
Replies
5
Views
2,496
Hi all, I need some local help to upload the Crimson program from a G310 Red Lion HMI. It cannot be easier than that. The thing is (for reasons...
Replies
6
Views
1,053
Hello: Working on a program that needs to read some data from other Rockwell PLCs. Every second my program sends "CIP Data Table Read" command and...
Replies
30
Views
6,927
I found these two software dongles in an old desk occupied by one of our automation guys. The black one looks like an Indusoft dongle but it...
Replies
10
Views
3,730
Hello Everyone. I know with Rockwell stuff, the series card is important, cant' just swap a series A input card with a serB, even if the catalog...
Replies
1
Views
1,896
Back
Top Bottom