Some background: We have two assembly machines in house that make a part that gets crimped by deforming the top of a cylinder. We use a LVDT with some tooling to examine the step height from the top of the crimp to the next component that is captured by the crimp and our operators use gauge pins to examine the diameter all to ensure compliance within limits.

I want to install a 3D sensor to perform the checks. I have a few picked out that show promise. The issue is the current level of communication on the machines which is DH-485 (currently only between an HMI and PLC). We have SLC 5/03's installed with some remote I/O as well. The leading sensor candidate that we are considering to purchase uses ASCII protocol over either ethernet or serial communication.

How do I get actual values from the sensor to the PLC for display on the HMI? I spoke to our controls engineer yesterday and he thinks a 'Basic' module like 1746-BAS-T would likely have to be added to the rack to capture the data and communicate with the sensor.

The goal is for an operator to examine the HMI for maybe a running average of the crimp or a measurement history so that they would be able to tell if the tooling is hitting too hard or not hard enough.

The controls engineer was also considering the possibility of swapping the 5/03's for 5/05's and upgrading to ethernet. Is there an advantage to this other than speed?

If anyone has any suggestions please let me know. Any help is appreciated! My apologies in advance if I don't respond to questions directly. We're pretty busy here.
 
I've used the SLC Basic module. Very old-school but works. Converting to 5/05 would be nice, but doesn't solve your problem.


You might consider switching the SLC's channel 0 to user mode, but that will make programming a pain. Unless your programmer has the funky serial-to-DH485 interface (I don't remember that model #).
 
Well it's good to know that the basic module is an option. Neither of us have used it before. I believe we do have the serial to DH485 converter. Just trying to figure out the best option for everything to talk.
 
The Basic module is good for simple coms i.e. ascii, quite simple to program you do not have to buy the basic configuration software can be done with a terminal program, the basic config software is expensive for what it is.
 
Good to know. I was just in the manual for the Basic module and saw that the programming software has it's own manual as well. Getting ready to peruse that to get an idea of what needs to happen.
 
All the 1746-BAS cards are obsolete and no longer being produced. I'm sure you can still purchase on the used/refurbished market, but that's just kicking the can down the road.



I would look into migrating to the CompactLogix family. You could use a 1769-ASCII or 1734-232ASC. In the compactLogix family, all the ascii programming is done in the PLC program, so it makes it much easier for a maintenance guy to troubleshoot or replace. You don't have take the card out and move jumpers around multiple times or load the BASIC program using PUTTY, Hyperterminal, or some other terminal software. You can use a 1747-AENTR if you want to keep your SLC Rack and I/O and not rewire. You will also gain ethernet connectivity, and it will all be cheaper than the retail price of a SLC 5/05. SLC parts are getting harder to come by and more expensive daily. I would take this opportunity to migrate for the future, especially if you already have a Studio 5000 software license.
 
The remote I/O is the "Flex I/O" RIO adapter and several input/output cards and my understanding is that it is not compatible with the Compactlogix platform in which case we'd have to replace it adding a fairly significant cost to retrofitting. This is the main reason I'm asking about possibilities for communicating within the SLC platform.
 
And to be clear, the vision sensor I'm looking at has ethernet I/P capability and that comm protocol would be preferred. I just didn't think they were compatible.
 
could go the route of upgrading to a compactlogix? replace all the racks rio with ethernet cards. convert the program to compactlogix program. Then you can use an up to date interface, but maybe this is too painful?
 
It's a money issue where I'm at. IMO it would be preferable that the two machines be brought up to a more current platform. At some point a third machine will likely be built and although some of the hardware in the machine would likely be vastly different (Ethernet I/P valve & sensor modules vs. wiring come to mind), the PLC platform could at least be the same. They might be able to share spare parts at a minimum or something along those lines.

There was also concern about cycle time with DH485 (1.5-2s-ish) and recommended an accelerator unit that would help with saving time @ a cost of $3500ish. I'm thinking 4 1794-AENT's and a Compactlogix would eclipse that but perhaps not by much.
 
And to be clear, the vision sensor I'm looking at has ethernet I/P capability and that comm protocol would be preferred. I just didn't think they were compatible.


Moving to a SLC5/05 won't help that issue, since the SLC family only has limited explicit messages only support. You may could let a CompactLogix do all the sensor communication and message the needed values to the SLC until you get the money to complete the upgrade, but none of the new CompactLogix family have builtin serial ports to communicate back to the SLC easily.
 
The local is a 7 slot rack. I agree. I think this and a Compactlogix is the way to go. Possibly with the adapter that will allow the Compactlogix to talk to the SLC rack that was mentioned.
 
Can you specify the 3D sensor so folks can examine what is serial and Ethernet protocol capabilities are ? Keyence, Basler, LMI Gocator, Cognex, SICK, IFM Efector... there's a few that come to mind.

The Channel 0 serial port on the SLC-5/03 and the string instructions in the SLC operating system can handle simple short (<82 char) strings of data.

In my opinion the 1746-BAS (or its sorta-modern successors, the Prosoft MVI46 modules) are mostly valuable for legacy support and heavy-duty hardware.

My first instinct is to go for a more modern middleware device that can handle both the 3D sensor's protocol and the SLC's data table access commands over DF1 protocol to the SLC's Channel 0 serial port. This could be a Raspberry Pi running Node-Red or Python, or a Red Lion DataStation, or a Hilscher or HMS gateway device, or something else.

I would start by establishing exactly what the 3D sensor offers: ASCII data sent as human-readable strings ? EtherNet/IP cyclic adapter functionality ? Emulation of ControlLogix tags ?
 
Ken,

The sensor we are looking at is the LMI 3500 series snapshot sensor. The manual simply says that it is capable of ASCII over ethernet or serial communication.

From the manual:

"The ASCII protocol is available over either serial output or Ethernet output. Over serial output,
communication is asynchronous (measurement results are automatically sent on the Data channel
when the sensor is in the running state and results become available). Over Ethernet,
communication can be asynchronous or can use polling. For more information on polling
commands, see Polling Operation Commands (Ethernet Only) on the next page."
 

Similar Topics

Hi All, I have a lifting/hoist application that I am using a powerflex 755 1hp drive. I am using a 1/3hp SEW gear motor that is rated at 0.57A...
Replies
3
Views
4,962
Greetings Gentlemen, I must admit I haven't worked much with analog output modules outside of controlling a VFD (and that was not in Omron) so...
Replies
5
Views
2,526
Hope someone has experience with this. We've recently upgraded a system at a remote site. This is a AB SLC 5/05 processor with two 10-slot...