SEW Inverter is accessible but not reachable in Tia
Acmesereno
Aug 2021
South Carolina
Technologies:
Tia 15.1 update 5
Siemens CPU 1517F-3
SEW MDX61B+DFS21B
From the TIA hardware configuration, the SEW drive is accessible from "assign name" and the status/name/ip are ok, but the device has the not reachable status in the main window.
The DFS21B has a red run light and red FS light which from the manual seems to be mechanical/electrical device error.
Are there any things I should try in software before replacing the card?
Technologies:
Tia 15.1 update 5
Siemens CPU 1517F-3
SEW MDX61B+DFS21B
In my experience, things need to match EXACTLY, and unfortunately there are no diagnostics for "these parts of the config match reality, but these don't". Sometimes it just doesn't work. I'd double check the device's config and make sure the GSD was built up correctly.
If you are using a managed switch such as SCALANCE X04, you could try getting a Wireshark trace of the communication in the state that you mention does not work as expected. The Profinet add-in for Wireshark is very good, and the trace may provide valuable diagnostics information. If you post the trace, then someone may be able to provide additional help.
What does the 24V operation of sew inverter mean? I can't make the inverter starting the motor
465
Hello, I have not programed plc wtih profibus communication yet, so If anybody has any idea how to please help. So I use PLC CX2020 and program...
2,362
I'm having a SEW Drive Inverter fault code: F14 which is a Encoder fault. The subcode that I have on movitools is the 27 Encoder error - encoder...
10,669
Dear colleauges,we have got a S7-300 plc and a SEW Inverter .Now there is a problem.When we give start to system firstly break enable signal come...
3,992
Hi, Im new here. I want to use a SEW Inverter as a drive for my Siemens PLC thru profibus interface. Do you have a program with start stop...
1,960