5069-SERIAL Add-on Profile V2.012

h_industries

Member
Join Date
Sep 2021
Location
Indiana
Posts
2
Does any one have a copy or a source for the v2.012 AOP for the 5069-Serial. If I go to the product compatibility and download center for rockwell, the module is there but if I click download, only EDS files are listed, no AOP. Studio 5000 is telling me the add-on profile is not installed
 
Try looking under 'Add-On Profiles' in the PCDC, there's a generic one where you can select from a long list of Logix 5000 AOPs.
 