ATV930 Programming to Control Logix Ethernet IP

jesusramos

Lifetime Supporting Member
Join Date
Apr 2017
Location
Kansas
Posts
3
Hi I’m having issues figuring out how to connect a Schneider ATV930 to Control Logix PLC.
Can’t figure out the Connection Parameters, I used the following.
Assembly Instance: Input: 100 Size: 8
Assembly Instance: Output: 101 Size: 8
Assembly Instance: Configuration 6 Size 0
Comm Format: Data-INT


I keep getting Module Fault Code (16#012a) Connection Request Error: Invalid output application path.

Please Help!
 
Last edited:
Assy inst INPUT = 101 Size: 6,
Assy inst OUPUT= 100 Size: 6,
Assembly Instance: Configuration 6 Size 0

Make sure to use SoMove and set ethernet to TCP/IP fieldbus
 
Thank You!!! tried it, and got it working, I appreciate your help, I'm glad I paid for the membership, Again Thank you!!!
 

Similar Topics

Hi I’m having issues figuring out how to connect a Schneider ATV930 to Control Logix PLC. Can’t figure out the Connection Parameters, I used the...
Replies
0
Views
996
Dear all, I have fx2n plc on my hand but I don't have the programming cable sc-09 and it would not be easy for me to get one. I need the cable...
Replies
3
Views
67
Hi all, i am the new controls guy at the plant and i have inherited a pc from the previous controls guy with Siemens tia portal version 16 and 17...
Replies
20
Views
707
I need to pull the program off of an old 90-30 so I can convert it to Allen Bradley. This is my first time messing with GE and I don't have the...
Replies
2
Views
83
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
Replies
9
Views
454
Back
Top Bottom