Fuel oil tank level
Good day everyone.
I have a pending project regarding tank level. This company wants us to set up a sensor for the amount of fuel oil in a single tank at any given time. Our idea as a company was to install a pressure meter at the bottom of the tank, in order to find the height of the liquid, then the volume. My question is the following: would a Siemens SITRANS P DS III sensor work for it, considering the liquid in question (fuel oil)? Would the sensor become corroded at all? |
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
![]() ![]() Join Date: Feb 2008
Location: OKC
Posts: 1,614
|
When we have level transmitters for oil tanks, we usually mount them on top of the tank (non contact). As you state, depending on what oil you are measuring, there could be corrosion.
I think this is the one we have used in the past: http://www2.emersonprocess.com/en-us...ges/index.aspx |
![]() |
![]() |
#3 |
Lifetime Supporting Member
|
If you are measuring oil level with a pressure transmitter make sure you know the specific gravity of the oil. If you are worried about corrosion use an isolation diaphragm similar to this: http://www2.emersonprocess.com/en-us...ges/index.aspx
|
![]() |
![]() |
#4 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2012
Location: Colorado
Posts: 1,530
|
What size is your tank? How accurate do you need it to be? Do you need to interface with a PLC or HMI?
__________________
There is never enough money to do it right but there is always enough money to do it again. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Jul 2015
Location: Fort Worth, TX
Posts: 2
|
It's a 2.5 meter diameter, 5 meter long bunker C fuel oil tank.
I need an HMI, and the purpose is to calculate the volume of oil in the tank. Is it a better idea to get an ultrasound sensor and set it on top instead? Last edited by tcarafi; July 10th, 2015 at 04:06 PM. |
![]() |
![]() |
#6 |
Member
|
Head pressure works for level, but the result is density/specific gravity dependent. Physical level (elevation) is a calculation: head pressure/specific gravity.
Say the level is constant but the density changes due to temperature. The indicated level (from the transmitter) will not change because the head pressure is the same, but the physical level will change due to the temperature related expansion or contraction. Corrosion is unlikely, because Siemen's wetted parts are at least stainless steel. |
![]() |
![]() |
#7 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2012
Location: Colorado
Posts: 1,530
|
That is a small tank compared to what I am use to.
You should have a bunch of options for a tank like that. You an use Float, Pressure, Magnetostrictive, Ultrasonic and Radar. A lot will depend on how accurate you want to be, what is available in your area and the budget. I would take a look around and see what you can get your hands on maybe call a local company that specialises in level measurement and see what they have.
__________________
There is never enough money to do it right but there is always enough money to do it again. |
![]() |
![]() |
#8 | |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2012
Location: Home
Posts: 139
|
How much do you have to spend??
I have used static pressure instruments in the lower part of the tank with good success. And you can make the display tell you how much is in the tank, and not have to HMI it?? John Quote:
|
|
![]() |
![]() |
#9 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2012
Location: Colorado
Posts: 1,530
|
One important thing: Make sure that you get a system that is rated for the hazardous environmental conditions of the material in the tank. If it is a vented tank you will need Class 1 Div.1 rated equipment if you will have any electrical connections on it.
__________________
There is never enough money to do it right but there is always enough money to do it again. |
![]() |
![]() |
#10 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2011
Location: Portland, OR
Posts: 408
|
I've used ultrasonics for this sort of thing (tank level measurement) on a few different projects and it's worked well. Pretty simple to program and install.
|
![]() |
![]() |
#11 |
Member
|
Is this a round tank with the axis horizontal?
__________________
Vaughn If you can read this, thank a teacher. |
![]() |
![]() |
#12 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2011
Location: Portland, OR
Posts: 408
|
|
![]() |
![]() |
#13 |
Member
![]() ![]() Join Date: Apr 2014
Location: Beaumont
Posts: 173
|
Up here we use Titan Logix TD-80 Level Sensors on fuel and oil trucks, great mobile product, good temp ratings, also Class 1 Div 2 rated for explosion risk areas. It uses Radar and time of flight to measure the distance from the top of the tank to the fluid level, volumes are calculated by the unit with a strap chart. To connect to an HMI, the unit comes with a 4-20ma output and I convert that to distance, from there I have a strap chart in the HMI or PLC.
Unit runs on 12-24Vdc, I typically use 24Vdc as the 4-20 seems to react better. There are probably hundreds of thousands of these units in service around North America, most oil field tankers use them, but they can be used on all types of fuel and water/liquids. The in-tank components are all stainless. Might look them up and see if that is what you need. |
![]() |
![]() |
#14 |
Member
|
be sure the tank has a pressure outlet on top, as otherwise you can measure wrongly with a pressuresensor.
__________________
shooter@home.nl skype shooter paul.deelen Computer Shooter Paul Deelen ![]() J. Wassenaerstraat 29 NL 5224 GG 's-Hertogenbosch +31653300739 |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
STUDENT QUESTIONS, please post them here! | Lancie1 | LIVE PLC Questions And Answers | 58 | February 6th, 2015 07:16 PM |
Advanced Control - Tank Level Control | Peter Nachtwey | LIVE PLC Questions And Answers | 22 | April 19th, 2014 04:22 AM |
Remote Sump and Tank Level Control, AB 5/04 | DiaperWolf | LIVE PLC Questions And Answers | 2 | March 7th, 2011 07:21 PM |
Fuel Oil | GregPLC | LIVE PLC Questions And Answers | 17 | December 2nd, 2004 05:44 AM |
tank level interfaces | Paul L. | LIVE PLC Questions And Answers | 8 | May 5th, 2004 12:20 PM |