Device net reads 0 ohms?

dhracer3

Member
Join Date
Jun 2015
Location
Asheville
Posts
12
Checking a device net and I'm getting 0 ohms on a network.
I'm sure this has to be an open wire correct?
I've check my cables but don't see anything out of the ordinary.
How do I check for an open along the cable?

Thanks.
 
Zero ohms would be a short.
Between what conductors on the cable?
Are you getting error codes on the scanner module ? What are they?
 