Powerflex 755 reverse direction while running
Osiaan
Aug 2017
Brisbane
Just wondering, what would happen if the direction is reversed while the drive is running, without the speed setpoint changing. Specifically, how would the S-Curve ramp behave? The drive is controlled via Ethernet/RSLogix5000.
If you had both Forward and Reverse inputs on at the same time the drive would ramp to stop at Dec rate.
If it was just Reverse input then the drive would ramp down to zero at the Dec ramp then ramp up to the commanded speed at the Acel ramp. the rive will not fault out.
the s-curve would be the same either way. As long as the drive doesn't go into regen mode and cause a buss over voltage.
Thanks, that's what I thought (hoped). So, just to confirm: S-Curve ramp to 0 at decel rate then another S-Curve ramp to setpoint at acel rate.
Will make my life a lot easier. As you might have guessed it's for a hoisting application and I just wanted make sure there will be a smooth transition from one direction to the other.
If is were doing a hoisting application this is the drive I would use without a second thought. they have all safety built in Proof of Torque, brake control, proof of brake, check for motor coupler failure.
http://www.magnetekmh.com
I know you like the Powerflex but check them out, way ahead of all the other drives,
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
257
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
166
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
134
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
224
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
422