Guys Good morning,

I have a question regarding Siemens micro memory card.

First i need to clarify my doubt why we use this micro memory card?

( i think after writing program we have to save program in micro memory card and than we can use this micro memory card to transfer program in CPU by plugging memory card in CPU)

If this is the function. So like Allen bradley can we use Ethernet cable in order to transfer program to CPU in Siemens S7 -300?

Waiting for your reply.
 
It is not quite like an AB PLC.
In an S7-300, the MMC card is mandatory. There is no backup battery.
In S7-400, there is a backup battery, and you can run it without an MC card.

If the S7-300 has an onboard ethernet port, or there is an ethernet CP module, then yes you can transfer the program to the PLC that way.
I strongly recommend to only consider ethernet-enabled CPUs. If an S7-300 with onboard ethernet is too expensive, then consider the IM151-8 (ET200S CPU).
 

Similar Topics

I have little unclear how this Siemens memory works. For now i have problem that my load memory (mmc) is over 80% full so i have to upgrade it to...
Replies
3
Views
2,369
I have a conundrum with this current circuit. I have a Siemens 1215C AC/DC/Relay and an old drive - Ratiotrol (now Boston Gear company I...
Replies
7
Views
1,146
Hi, I'm new to this forum and have been programming plc's for about 2 years now. I have done programming and mods on different small systems and...
Replies
3
Views
3,296
Just when you think your problem is solved..... new problem! My Siemens rep came through with with the Step7 Micro/WIN software I needed for a...
Replies
4
Views
6,852
I have an opportunity to quote an HMI project for one of my customers. It's a small project, and the customer is not the type with deep pockets...
Replies
3
Views
24,756
Back
Top Bottom