I had a panelview C600 get wet and smoked it. I got another one, and thankfully I was on the ball and had the program backed up. So I loaded the program into the new screen, and installed it. My problem, I failed to change the IP address, now I cannot communicate with my plc, and I cannot access my configuration screen since it is password protected. Is there anyway to hard reset this screen? Or, access my configuration screen, easily?

This is a PanelView C600 cat. 2711C-T6T.
 
Hello swtjhny,

there is another way to go to the config screen.

On a usb stick, create a autorun.bat. Even with no code.

Put the stick into the panel and it asks for autorun.
Select "yes" (F1).


Best regards,
crawler009
 
Attatching the USB keyboard to the c600 and using the ctl+shift keys at boot up worked. Thank you very much.
 

Similar Topics

Have a C600 Panelview that the display went out in it. It still has the configuration in it and the equipment is still running. Believe it is just...
Replies
2
Views
1,592
I have a working collection of applications for the PVC C600. the setup is one pvc600 connected to a DH485 network with two micrologix 1200's...
Replies
3
Views
1,561
Hi Guys, I have a Panelview C600 2711C-T6C that one of our clients have and they wont to remote access the screen is there anyway you can do this...
Replies
2
Views
2,900
Afternoon folks, Anyone have any idea where I can find the download for USB RNDIS driver to connect to a C600 Panelview. Looked everywhere and...
Replies
4
Views
10,219
I recently bought a C600 and I setup the communications so that I could program it throught the ethernet port. I completed a reboot of the system...
Replies
2
Views
2,476
Back
Top Bottom