Micrologix 1000 DC COM

mavrick

Member
Join Date
Jun 2015
Location
usa
Posts
122
I have searched every where but cant seem to find the answer. Is the DC COM terminal on a Micrologix 1000 controller internally connected to the inputs?

I'm wanting to install a pnp sensor and the manual request you take a jumper from the 0vdc(-24) from the 24 volt power supply and land it on the DC COM terminal.

I'm trying to understand why and what is it doing? Thank you
 
With the 1000 you can use your own external power supply OR use the on board supply as long as your needs are within it's power limit.
The DC Com is for a group of inputs, on larger units there may be more than one group so more than one DC com.
 
I may have missed spoke. I'm trying to understand how the DC COM terminal operates. Is it internally connected to the related input group or is it just there to be utilized as a isolated jumper terminal to supply 24 volts. to my sensor.
 
I miss spoke on my original post . The manual request you terminate the 24vdc+ on the DC COM. for pnp. That is where I'm confused is why does the DC COM need 24+? Couldn't I just supply my fiber senor the 24+ and 24- from the dc power source and the take my switch leg to input I/4? Thank you for the help.
 
The DC COM terminal is a point of reference for its associate group of inputs. If you take the DC COM terminal low, then a high signal at an input point will be "true". If you take the DC COM terminal high (+24vdc) then a low signal at any of its input points will be true. There must be a difference in potential between the DC COM and its associated input points in order for it to detect a "true" signal and place a "1" in its memory location. If there is no difference, you will get a "0".
 
Thank you OKIE PC. That's what I was looking for. That makes sense as to why the DC COM is needed. Thank you all for the help!
 
Spot the difference?...

parky said:
See this from Rockwell page 2.3 it shows you the connections for sink & source

https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1761-um003_-en-p.pdf

Hi,

Just be careful with that sample reference for a 1761-L32BWA controller. The wiring diagram is correct but the wire descriptions are a bit mixed up for the lower diagram on Page 2-3.

If we use Publication 1761-IN001 - MicroLogix 1000 Programmable Controllers Installation Instructions, and refer to the same 1761-L32BWA example wiring diagram on Page 19, we will see the correct descriptions for the wires. This is with respect to VDC +/- and Sinking/Sourcing.

I just wouldn't want anyone to find that the above "Sourcing" leaves them with a "Sinking" feeling.

Regards,
George
 

Similar Topics

I have a customer that was troubleshooting an issue with communication loss with a PanelView and MicroLogix 1000, I think they were just trying...
Replies
6
Views
5,854
I've got a Micrologix 1000 that I seem to have lost communications with. I was able to AutoConfig using RSLinx, and then the problems happened...
Replies
10
Views
6,100
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
124
Hi all, We have a very old pit pump system running on Micrologix 1000. Now, whenever there is an alarm for high conductivity, we want that alarm...
Replies
5
Views
1,254
Looking at a Micrologix 1000 1761-L32AWA, I tried to connect using the 1761-CBL-PM02 through a Serial to USB converter (This setup was used...
Replies
2
Views
982
Back
Top Bottom