Factory Talk ViewSE Data Logging to File - change of datatypes

mzurtak

Member
Join Date
Jun 2015
Location
Canada
Posts
2
Hi,
I have a clients machine running Factory Talk View SE release # 8.00
I have set up trending and data logging which has been working correctly for the past 6months until 48hrs ago when the data logging to file set has changed half of the tag data types in each set from analog tags to string tags. I confirmed this by looking at the log files. Creating new log files using the "NewDataLogFile" command did not fix the problem.

Firstly how would I go about changing the tag types back to Analog tags? Would this need to be required to be done in the 'SQL Server Database Primary Data File'.
Secondly does anyone know why the data types would have changed and are they set by data coming from the PLC? Becasue I cant set the data type for each tag in the Data Log Model setup.

Thanks
 
So called tech support... it is a known problem for FactorTalk View SE. It is caused when the Sever looses connection to the PLC and when reconnect some of the tags comeback in as Strings rather than analog floats.
To fix restart the server/computer.

ItCrowdMEMS.jpg
 

Similar Topics

Well, after straightening out all of my Factory Talk password issues, I decided to install the patch roll-ups for RSview SE. The installation...
Replies
7
Views
6,328
Hi Friends; I have a red Explanation Mark on Factory Talk Directory in Task Bar. Before Update the windows and installation of AutoCad it works...
Replies
1
Views
73
I am trying to enable an external alarm via computer speakers for Factory Talk Network Distributed Edition. I am using Alarm and Events setup. I...
Replies
7
Views
161
We have a quad monitor setup with FT SE and we are utilizing a header screen at the top of every display. when we open a new page we abort the...
Replies
0
Views
88
Good day colleagues, I have a problem with a plc slc 5 since I export the tags to my factory program to load them into a panel view 1000 plus 6...
Replies
0
Views
104
Back
Top Bottom