Symbol Descriptions RSLogix 500

ajb1131

Member
Join Date
Feb 2006
Location
Minnesota
Posts
3
I was wondering how to view the descriptions in rslogix 500.
When i go online i cant see them.

Thanks
 
Last edited:
Right click on any blank space in the ladder editor window.

Select "Properties"

Select "Comment Display" tab.

In the "Symbols" areas tick the "Show Symbols" box, then
you can choose either "Show Addresses and Symbols" or "Show Symbols Only"

(Personally I prefer to put Symbols on everything and select "Symbols Only" and that way I don't have to think too much about the Addresses.)
 