0-5 vdc for calibration

Amazon do a 0-5v 0-10v & 4-20ma generator, providing you do not need UKAS or other type certification should be ok & cheap too.
 
Are you actually going to use it for calibration, or just for getting analog circuits to about-the-right levels ?

If you need NIST-traceable calibration, don't buy some cheap voltage regulator with a dial and display off Amazon.

The PLCCable device is fine for ordinary stuff; 1% full scale is plenty accurate for a lot of sensor and PLC applications and they're a good company run by a member here.

But if you need 0.01% accuracy and a traceable calibration certificate, you're going to need to pay more for a mainline device.
 
Thanks for the replies.
My need is setting the span and zero of a panel meter for a reference reading.
Absolute precision is not required.
One of the inexpensive models will work for a down and dirty setup.

I do, however, have other needs for a more precise set up, so I will look into purchasing that Extech model that Ken mentioned also.
Again, thank you to all of you for the help.
 

Similar Topics

I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
Replies
10
Views
417
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
Replies
1
Views
107
I have a conundrum with this current circuit. I have a Siemens 1215C AC/DC/Relay and an old drive - Ratiotrol (now Boston Gear company I...
Replies
7
Views
1,169
I have begun using 480VAC power supplies in my panels to keep heat from a transformer out of the panel. This works great if the panel is mounted...
Replies
17
Views
4,133
Good Afternoon , It seems like we always have problems with using Type J Thermocouples with our slip rings . Would using a RTD at 10...
Replies
6
Views
1,638
Back
Top Bottom