Powerflex 525 Does Manual Mode Exist?

Sym_Boots

Member
Join Date
Aug 2021
Location
US
Posts
12
Does anyone know if the Powerflex 525 has a manual mode option like Powerflex 753s do? For the Powerflex 753 I am using a 20-750-ENETR module to communicate with my PLC and reading the Logic Status word bit 9 to tell if the drive is set to manual by the HIM or not. I cannot find a similar status or parameter in the powerflex 525 manual and I am wondering if I am not looking in the right spot. Does anyone know if a similar function exists with the 525 and what it would be called?
 
Have a look at parameter B012.

You can also use bits 8 (ENetSpeedCtrl) and 9 (ENetLogicCtrl) of the LogicStatus word. The only inference you can make from them is that drive control comes from *something* other than ENet, such as the drive's terminals or the keypad itself.

525B012.PNG
 

Similar Topics

Good Morning , I am working on a project with some PowerFlex 525 drives. I am using CompactLogix 1769-L18. I took notice that the tags that...
Replies
23
Views
22,486
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
217
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
2
Views
224
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
Replies
9
Views
456
Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
Replies
4
Views
221
Back
Top Bottom