Hi Guys!
1. Can a FTV ME Tag bearing '::[Path]Address' format communicat with Emulate500/RSLogix?

2. Secondly, if N10:45 has just two of it's Bits used (ie N10:45/0 and N10:45/1) in that word, and N10:45 is tied to a tag in HMI with Multistate Indicator having 4 states in 'states' tab, How will the used Bits point to the 4 state values? (ie what Bit points to state0, state1, state2 and state3 respectively)?.
 
Yes you can use emulate 500. What I usually do is delete the shortcut in communication setup. Then add a server to the project with the same name as the shortcut you just deleted and is referenced in your project. You then setup this server to use linx, you will have to setup a topic within linx. It's not the most intuitive, but once you've done it a few times it only takes a minute or so to setup.
 
Secondly, if N10:45 has just two of it's Bits used (ie N10:45/0 and N10:45/1) in that word, and N10:45 is tied to a tag in HMI with Multistate Indicator having 4 states in 'states' tab, How will the used Bits point to the 4 state values? (ie what Bit points to state0, state1, state2 and state3 respectively)?.

Here's one possibility that immediately comes to mind:

00 == 0
01 == 1
10 == 2
11 == 3
 
It seems the bit array stuff is still kicking your butt. You are making it way more complicated then it has to be. He's an example:
1. N10:45/0 is automatic mode
2. N10:45/1 is manual mode

Use expressions in the multistate:
1. State 0 = Off
2. State 1 = Auto
3. State 2 = Manual

So...
If N10:45/0 Then 1 Else
If N10:45/1 Then 2 Else 0

This is assuming bit 0 and bit 1 will not be on at the same time.

Spend time playing around with this, the more time you spend the more sense it will make.
 

Similar Topics

Hi Friends, I am setting up Panel PCs to run SE Standalone, and I have some questions that I was wondering if anyone here could answer from...
Replies
2
Views
1,045
I have a question about parameter files in Factory Talk View Machine Edition. Can you pass placeholders in a parameter file like you can with a...
Replies
2
Views
1,745
I'm pretty sure the answer is no but I'll ask anyhow. I (we) use multistate indicators to display sequence steps as a machine gets to them...
Replies
6
Views
2,450
Hi, good afternoon all. Do you know if I need a specific version of Factory Talk View to program with Visual Basic?
Replies
1
Views
1,362
Hello, Just signed up and thought I would just jump right in and start asking questions. I work at a water plant as an operator, and am also...
Replies
2
Views
1,770
Back
Top Bottom