I have a problem with a line of code I am trying. I have an output i need to energize for two seconds and then drop out, although the input that is associated with the output will remain true. I was able to acive this with the code I wrote, however on the next scan the output went high again. I am sure there is a simple way to do this, however everything I have come up with is complcated. I am using RSlogix 500 with a micrologix 1000. Any ideas would be great. I am sorry, I cannot post the code I have written so far as I am not at the office.

Thanx
 
In RSLogix, double click on the rung number for this rung. The line of mnemonics will pop up. Please cut and paste this line into a post so that we can look at the code.
 
In my example, no matter how long B10/11 is true, B10/10 will only be energized for 2.5 seconds.



Hope this helps,
Paul
Paul, you are not using a (res) you are relying on the true false rung transision of B10/11 to reset the TON?
 
rung 1 XIC I:0.0/1 XIO I:0.0/2 TON T4:1 1.0 1 0

rung 2 XIC T4:1/TT OTE O:0.0/0

If XIC I:0.0/1 stays true and XIO I:0.0/2 toggles the timer will reset. yes?
 
I feel like my avatar today.........my house was broken into last night, and I only got a 1/2 hour of sleep
 
rung 1 XIC I:0.0/1 XIO I:0.0/2 TON T4:1 1.0 1 0

rung 2 XIC T4:1/TT OTE O:0.0/0

If XIC I:0.0/1 stays true and XIO I:0.0/2 toggles the timer will reset. yes?


Yes -- if EITHER I:0/1 or I:0/2 toggles, the timer will reset.
 
why not use 2 rungs.
rung 1 input turns on, then a one shot and then a tof timer set for your required time.
rung 2 timer dn bit turns on output

as long as the input stays on, the timer will only work once.

regards,
james
 

Similar Topics

It's been a long time since I played with an old PV1000. With the momentary pushbuttons, is there really no way to let you push/hold a button...
Replies
12
Views
2,926
Hello everyone, Does anybody know if there is a way of simulating the behaviour of a FTV momentary push button on iFix? I am trying to create a...
Replies
5
Views
1,733
I have GE iFIX 6.1. I have several PBs on my screens. I use the "click" option and select ToggleDigitalPoint. But this not what i want. As i have...
Replies
5
Views
1,785
Hi All Could anyone advise me on how to protect the push button on the screen from occasional touch? I've faced up the problem that I can't...
Replies
22
Views
6,394
For reasons, I find myself having to disable buttons using SE controls rather than in the PLC (massive project, no time to edit PLC properly). I...
Replies
0
Views
984
Back
Top Bottom