2wire inductive sensor rated 90-250vac

emeka

Member
Join Date
Dec 2012
Location
lagos state
Posts
34
Hi guys,i av a two wire inductive sensor rated 90-250vac...please how do i connect the sensor to the mistubishi plc...i am used to the three wire type of sensor of 24vdc....please i need help...
 
If the mistubishi plc inputs are 24VDC you can´t. Connect the sensor to a 230VAC relay and wire the relay contac into the PLC input.

How to wire the sensor:
One side of sensor to L1, the other side of sensor to relay A1 and the A2 of the relay to N.
 