0 to 5v anolog scaling question.

Icemanwillis

Member
Join Date
Sep 2022
Location
Alabama
Posts
3
Hi everyone. I am hoping that someone could assist me on some scaling. I have a 0 to 5v laser potentiometer that I am trying to scale into a PID. I am either not getting an output on the PID or if I do the fluctuations are crazy and all over the place. Utilizing TIA V13 the current Controls Engineer has the scaling set from 0 to 27648 to me this doesn't seem correct as that would be scaling for 4 to 20mA and not for an anolog 0 to 5v. Would I be correct in assuming this? I am learning as I go and just can't wrap my head around using a scale so high. Thanks
 
A few modules behaves differently, but 0 to 27648 is the range after the ADC for all 'normal' measuring ranges in Siemens PLCs.
What is the exact PLC hardware being used ?

I suggest that you trace both raw and scaled value. Maybe the signal from the laser is erratic ? Can you rule out noise ? A 0-5V signal is less noise resistant than a 4-20mA signal.
 
Thank you for replying. I believe I have the issue resolved. But to answer your question it is a Simatic S7-1200 with 1214CPU and SM1234 AI/AQ
 
Thank you for replying. I believe I have the issue resolved. But to answer your question it is a Simatic S7-1200 with 1214CPU and SM1234 AI/AQ
It is good forum etiquette to state what the problem was and what you did to resolve it.
edit: and for that module working in 0..5V mode, the raw unscaled value range is 0..27648.
 
Last edited:

Similar Topics

Can anyone help me with programing my first anolog circuit. I have a micrologix 1200 and an allen bradley power flex 4 VFD. I do not know what I...
Replies
8
Views
2,898
We have Allen Bradley 1756-if16 1.1 anolog input card. I need to zero out one of the inputs right now I am sending it 4ma I need that to be...
Replies
1
Views
1,599
Hello friends help me how to use analog in put in my ladder diagram in S7300? Thanks Usman
Replies
9
Views
2,175
Does anyone knows how can i scan many analog signals with only one analog input?
Replies
7
Views
2,412
Can anyone give some examples on how to program anolog input into a AB PLC500
Replies
1
Views
1,903
Back
Top Bottom