Modicon Quantum: Remote I/O Rack Problem (IOs communication or Drop-out)

esotericstone

Member
Join Date
Mar 2022
Location
Paistan
Posts
1
System Details:
We use hot redundant Modicon Quantum PLC with dual redundant communication having Remote IO racks (using CRP + CRA cards and coaxial cable). One rack is for Hot Redundant CPUs and other 12 racks are for Remote IO Drops (total 13 Drops). The model numbers of installed cards are given below

CPU: 140 CPU 434 12A (486 Controller)
RIO Head: 140 CRP 932 00
RIO Drop: 140 CRA 932 00
Software: ProWORX 32
Dual redundant communication using Coaxial Cable and splitters

Problem Faced and Action Performed:
A. Our plant was running and tripped without any process abnormality. Most of inputs configured in different DI cards of the rack 2 actuated at the same time, which triggered the tripping. The same was diagnosed from the alarms history on HMI. No evidence of system / rack failure was found on CPU/CRA/CRP or HMI.

We replaced the CRA (RIO Drop) card of the rack 2, as this could be the single point of failure.

B. The plant was started again, but some hours later, the same nature of problem and alarm from inputs of DI cards were observed.

This time the Drop's back-plane and DI cards of actuated inputs were replaced.

C. The plant was started again and to our surprise, tripping happened again after a few hours with same alarms .

Upon further troubleshooting, PLC Status tab of ProWORX 32 an Overrun error in word #175 and word #178 were found.

Based on the errors, PV and SV versions of CRA cards of all racks were compared. Their SV versions were in the range of 1.XX. whereas the only 1 CRA card had the SV of 2.00, which was replaced initially during Action mention in para A.


Therefore, the card with SV2.00 in drop 2 was replaced with SV version 1.26.

D. After this activity the plant was started again and is running in normal state till the time of writing .

Questions:

  1. - What could be the possible causes of these nuisance trippings?
    - Can the difference in PV and SV versions of CRA/CRP card, result in such trippings ? If yes, Is there any compatibility matrix.
    - What is probable cause of Overrun Error ? Is there any relation of this error with these trippings?
    - Do you have any case study and example of such nature of trippings?
 

Similar Topics

Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
Replies
6
Views
259
Hi There, I have a Modicon Quantum PLC, there is a alarm on display "noConfig" its happened after power failure, I have gone through manuals...
Replies
3
Views
650
When i read the specification of 140CPU43412A i observe that as remembered in specification 1. Local i/o : Maximum i/p and o/p words are 64 in...
Replies
0
Views
495
Main rack contained power supply 140cps52400 and 140cpu43412A and RIO HEAD 140CRP93100 in addition to another I/o cards . Another remote rack...
Replies
8
Views
1,860
We are now planning to upgrade from Quantum 140CPU11303 to Modicon M580. The software protect was written by Proworx NxT (.DCF). Is it possible...
Replies
1
Views
1,001
Back
Top Bottom