Hi All,
I have to make a beep sound when an alarm from priority 1 appears. I will use Playsound() function, but I face the problem of how to get the information whether any alarm from priority 1 appears. Do You know how could I get that information in Intouch. I use Intouch 10.1. Thanks in advance

Best regards
Karol
 
Yes, this is an old post but I was looking for precisely this earlier today and finding the solution took a while.

Create the below QuickFunction, call it from the 'WhileShowing' window script of the alarmViewerBar window and test the return value to call Playsound():

DIM HighPriorityAlm AS DISCRETE;
DIM NumOfAlms AS INTEGER;

NumOfAlms = #AlarmViewerBar.UnackAlarms;

IF NumOfAlms > 0 THEN
DIM Index AS INTEGER;
DIM NewAlmPriority AS MESSAGE;

FOR Index = 0 TO NumOfAlms
NewAlmPriority = #AlarmViewerBar.GetItem(Index, "Priority");

IF NewAlmPriority == "1" THEN
HighPriorityAlm = 1;
EXIT FOR;
ENDIF;
NEXT;
ENDIF;

RETURN HighPriorityAlm;
 
Last edited:

Similar Topics

Hey guys, I'm trying to write a script that auto-restarts Win-911 if it crashes. I've gotten that to work, but the problem is that my client has...
Replies
3
Views
3,359
Hi all, I'm trying to check the health of the main and failover servers in a Terminal Services Intouch installation. There are 2 servers, each...
Replies
0
Views
1,930
Hey all. Ive got a screen where an operator is going to scan in with a bar code reader 140 serials. They click the position a serial goes in (it...
Replies
13
Views
5,184
Trying to export a Modern application for an upgrade to Intouch 2020 but I cannot export the application from the 2014 version because the export...
Replies
2
Views
91
Hi guys, I have experience with PLC to Excel etc...just starting on using intouch scada screens. I have an Excel sheet that uses mainly...
Replies
1
Views
129
Back
Top Bottom