ControlLogix Online Indicators

At least one of the I/O connections is not available. This, at least in this configuration, is not enough to prevent it going into 'Run' mode or causing a fault, but the equipment may not operate fully. Look at the status icons in the I/O configuration for the problem items.
 
That can also happen if you have a communications module listed in the I/O tree, with nothing connected to it in the I/O tree. The usual culprit here is the Ethernet module. There is no reason to list it in the I/O tree unless you are using it for remote I/O or produced/consumed tags.

If it is listed, with no partner, it will give the blinky I/O light warning.
 
The I/O light will also flash if you have Consumed tags that are not being consumed (e.g. the producer is not there, or there is a configuration error).

Look in the I/O Configuration area of the controller organiser, and follow the warning triangles to the module that is in error, double-click it to bring up the Properties dialog, then choose the "Connection" tab. On there you will see what the fault is.
 
That can also happen if you have a communications module listed in the I/O tree, with nothing connected to it in the I/O tree. The usual culprit here is the Ethernet module. There is no reason to list it in the I/O tree unless you are using it for remote I/O or produced/consumed tags.

If it is listed, with no partner, it will give the blinky I/O light warning.

I've never seen that happen... Which comms module(s) is this relevant to?

I've just tried it with an ENBT in the configuration, with no children, and no I/O errors are present.

2014-07-15_204543.jpg
 
Last edited:
I've never seen that happen... Which comms module(s) is this relevant to?

I've just tried it with an ENBT in the configuration, with no children, and no I/O errors are present.

If there is a 1756-DHRIO included in the I/O tree and is used only for DH+ it will cause the I/O light to blink.
 

Similar Topics

Does anyone know of a way to detect if someone is online with the controller in ControlLogix (from logic) I'm thinking that maybe there is a CIP...
Replies
7
Views
377
Are any of you guys out there aware of a consolidated list of I/O cards that can be replaced online? We just replaced a 1756-IF16 card while the...
Replies
2
Views
1,518
Hi I'm trying to change the scale in a analog Input module in the module while online. I got a warning saying something like Module changes could...
Replies
4
Views
2,056
Good Afternoon, I should know the answer to this . I have a 1756- 4-20 ma input card with spare inputs .I would like to add a new Analog...
Replies
3
Views
1,848
Is it true that you don't get the green True/False bars in "Online" mode on every element type? For example, the GTEQ or NEQ block: it doesn't...
Replies
3
Views
3,463
Back
Top Bottom