HSIO configuration w/no physical wiring

Pumba

Member
Join Date
Nov 2017
Location
OHIO
Posts
24
Found a program with some HSIO configuration using V memory setup. The problem is that there is no physical wiring coming from the inputs being referenced in the setup instructions. Is it necessary to have the setup instructions? The instructions are leading to a HSC. The V memory location is referencing that the count-up pulse is used as X0. But, after a examination of the wiring, there is nothing going to X0. Same situation with the reset V memory (X1): there is no wiring. I am using a DL6 program. And the machine is running fine. I am just wondering if the HSC is actually doing anything at all, and if not, is it even necessary to have it.

Thank you
 
It may have been used in an earlier version of the program. But note that the high nibble of the word sent to V7633 contain bits which control the monitoring of the battery and the power-up mode. See page E6 of the DL-06 manual.
 

Similar Topics

Hi All, I've also posted this at the AutomationDirect forum. I'm casting for as wide an audience as possible. I am attempting to operate a...
Replies
6
Views
2,491
Hi buds, I am wandering if you know of a way to look at the current Pulse Rate while doing a Trapesoid move for a Stepper using DL05. The...
Replies
0
Views
1,526
Hello I have a sensor that I read data with IO-LINK but I don't know how to get my data. I see that I have two modes : Process data Map0 and Map...
Replies
0
Views
8
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
Replies
2
Views
48
Hi All, Has any of you tried to change the IP Gateway of the PLC (of course, essentially of the ENBT card), while in a redundant configuration...
Replies
3
Views
117
Back
Top Bottom