Hi,

I would like to know:

A motor running on 30Hz

Or a motor running on 50Hz (nominal frequency)


Wich one will take the most current when both have to do the same job.

With 30Hz and lower voltage => will this one take the most current ?
 
Hmm,

I'm reading it, but reading many opinions...


Eurm

It's a motor that can be loaded very hard...

With the same load, 30Hz or 50Hz... Wich speed wil take less current...

I also think like: 220V and 380V motorconnections, 220V takes the most current.
 
When you are using an VFD and motor you can't look at it like a dual voltage motor. You aren't changing the motor wiring at any time while you are running the motor from the drive. Changing the motor wiring on a dual voltage motor is what allows the higher current level at lower voltages.

Below base speed an AC motor is essentially a constant torque device. Motor torque is based on motor current. You cannot go over the motors rated current for any extended period of time. So, assuming that your load is a constant torque load, the motor current will not be significantly affected by speed. Most conveyor application, hoist applications and some surface grinding applications are constant torque.

If your load torque is changing with speed then your motor current will also change with speed. You need to separate the causes, though. Then motor current is not changing due to any spoeed related phenomenon in the motor. It is changing because the load torque is changing. Centrifugal fans and pumps are examples of loads that change with speed.

Then there are center winders. These will appear to exhibit both qualities depending on how you look at it. For any given roll diameter the current does not change with speed. For any given web speed the current does change with roll diameter. The confusing thing is that winder motor speed changes with BOTH line speed and roll diameter. Again, make sure you separate the phenomena before you evaluate.

I have seen cases where the motor current rises very slightly as speed decreases. I believe this has more to do with current measurement filtering than anything else. If you are using at least a decent closed loop vector control or a good quality sensorless vector control the motor current should be relatively constant.

Keith
 
To expand a little on Kieth's comments, you have to look at the load, the motor, and the drive as a system. It is impossible to make a general statement about voltage or torque or horswpower or kW without defining the complete system AND identifying the point of measurement.

For example, in a constant torque load the motor current may be almost identical at several different speeds even though the voltage drops. With a variable torque load the motor current drops approximately as the square of the speed through much of the speed range. In some cases the current at the input to the drive will not track motor current exactly.
 
Tom makes a very good point here. I assumed that Combo is looking at motor current. However, he may be looking at drive input current. Keep in mind that drive input current will not match motor current.


Keith
 

Similar Topics

People always say how bad it is to start and stop motors frequently, question is, how bad is it and where do you draw the line. For example, I...
Replies
7
Views
2,113
My job is to try to control brushless servo motor with frequency inverter. I just connected such motor to a frequency inverter and I tried running...
Replies
10
Views
3,038
Do you folks know of any Motor Frequency Meters that have a 4-20 ma output ? I know a frequency drive would provide that need , but the customer...
Replies
10
Views
2,497
If u check on a AC motor name plate, u get certain information like Motor Rated Current, Supply Voltage, frequency etc. My question 2 u...
Replies
26
Views
7,599
I am helping out a friend that recently purchased a piece of old wood working equipment. I was told that the motors on this piece of equipment...
Replies
16
Views
11,747
Back
Top Bottom