Powerflex 755 Specialty Modules

Join Date
Dec 2010
Location
Burlington, NC
Posts
402
trying to install a 20-750-2262-2R in a Powerflex 755, I installed, now trying to access i/o in Logix 5000, cannot figure it out. I set up the module in the data links in the drive parameters but cant figure out how to set them up in Logix
 
Last edited:
Last edited:
For setting up the PF755 Datalinks on the controller side, open up the Offline RSL5K/S5K drive's module Properties/General Tab and choose the Change radio button; in the upper right corner of the applet check the Datalinks enable option and then list the Inputs and Outputs (CPU perspective) of the PF755 defined Input and Ouput assemblies and the linked PF755 parameters.
Save and then Download to the CPU.
 
Thanks DM,

This only our second 755 and we did not use an option card in the other one. We will be able to do our download when production is done for the day.

You're welcome Mark!

Just make sure you perform the PF755 Module edits onto an Upload/Online Save with Data Upload performed after the production had ended.

Not nitpicking...:D...Just remembering personal history...:unsure:
 
Last edited:

Similar Topics

So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
2
Views
34
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
Replies
5
Views
101
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
104
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
Replies
3
Views
199
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
Replies
10
Views
389
Back
Top Bottom