Old December 6th, 2017, 05:02 PM   #16
lesmar96
Member
United States

lesmar96 is offline
 
Join Date: May 2017
Location: PA
Posts: 124
That is a very good point which I hadn't thought of. The drive was not originial and when the drive was installed, they used the same CT. I cannot say at the moment, but I am quite sure, though, that the CT is on the line side of the drive. That would make some difference, right, or would noise, etc. still mess it up?
  Reply With Quote
Old December 6th, 2017, 05:49 PM   #17
osmanmom
Member
Malaysia

osmanmom is offline
 
Join Date: Mar 2014
Location: JOHOR
Posts: 1,381
Re-tighten all terminal screw.
  Reply With Quote
Old December 6th, 2017, 06:09 PM   #18
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,364
If the CT is on the line side of the drive, you're unlikely to get any meaningful data at all. If your low limit hasn't been changed since the drive went in, you'll absolutely have problems.

I once saw a VSD reporting 75A, but the power meter on the main incomer was only reading 40A. That's the sort of efficiency gains you can get out of a VSD. A CT on the line side of the drive won't really tell you anything about what's going on on the load side.
  Reply With Quote
Old December 6th, 2017, 06:28 PM   #19
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,249
Quote:
Originally Posted by ASF View Post
If the CT is on the line side of the drive, you're unlikely to get any meaningful data at all. If your low limit hasn't been changed since the drive went in, you'll absolutely have problems.

I once saw a VSD reporting 75A, but the power meter on the main incomer was only reading 40A. That's the sort of efficiency gains you can get out of a VSD. A CT on the line side of the drive won't really tell you anything about what's going on on the load side.
I disagree. You won't get an accurate motor amperage reading from a CT on the line side of the drive, but the signal that you do receive will tend to represent power in vs. power out.
__________________
  Reply With Quote
Old December 6th, 2017, 08:13 PM   #20
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 188
$20 says it's marginal in the summer, and below the threshold in the winter..

The new motor is more efficient than the old, so they had to slow it down. It now draws less current (line side), thus the trip. In the winter the motor and the drive are cooler and slightly more efficient. Therefore, it
s now under the trip point.

My guess anyway.

Just check the normal running current and readjust the sensor for the new load. Then go have a beer
  Reply With Quote
Old December 6th, 2017, 10:37 PM   #21
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,364
Quote:
Originally Posted by Bit_Bucket_07 View Post
I disagree. You won't get an accurate motor amperage reading from a CT on the line side of the drive, but the signal that you do receive will tend to represent power in vs. power out.
Well, true, you'll get something loosely proportional to the output power from the VSD to the motor. But in this application, it's not really of any use.
  Reply With Quote
Old December 6th, 2017, 11:53 PM   #22
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 578
The thing about CT's is they are designed for 60 hz AC when you start getting down to say 40hz the coupling will act more and more like DC the same with an increase in hz say about 70 or so. DC is not coupled through a transformer so you will show low current.

Most CT's are mounted on the load side of a contactor, it's jut easer that way the wire are readily available and you have more room in panel. So mu guess is that they are mounted o load side of the VFD in the new installation witch would mean that the reading you get from are next to worthless.
Just connect the input to the PLC to the analog output of the VFD ( set you for load) and I would bet you will see a big difference.
  Reply With Quote
Old December 7th, 2017, 05:34 AM   #23
dakota4065
Member
United States

dakota4065 is offline
 
Join Date: Dec 2015
Location: Shelby MI
Posts: 8
Is this a line shaft turbine or a submersible pump. Is the pump and motor inside or outside. If it is a line shaft turbine I would check the packing box to make sure there is enough grease and it has no water in it.
  Reply With Quote
Old December 7th, 2017, 09:49 AM   #24
shooter
Member
Netherlands

shooter is offline
 
shooter's Avatar
 
Join Date: Sep 2002
Location: duketown
Posts: 2,601
Where is the one way valve, when it is cold it can leak, thus the water pressure is low, and the pump will be low on power.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
  Reply With Quote
Old December 7th, 2017, 10:51 AM   #25
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,798
Water temperature at the pump itself won't change much winter to summer at 100 ft + deep.
My guess is that the foot valve (check valve) is holding water in the discharge pipe, and somewhere in the discharge piping there is a location that is freezing.

Most VFDs will let you set the analog output to give an amp signal. I would use that instead of a C/T for current indication.
  Reply With Quote
Old December 8th, 2017, 10:16 AM   #26
lesmar96
Member
United States

lesmar96 is offline
 
Join Date: May 2017
Location: PA
Posts: 124
Thanks for all your suggestions. Sorry for my absence and not answering your questions.

I definitly and going to make a couple changes. I can easily see why a CT could not read accurately on the line or load side of a drive. I will switch to the analog output of the VFD. But I don't understand why that works all summer and has a fit in the winter! Some things are hard to explain, I guess.

I also plan to add more of a delay for low current before it actually shuts the pump off. I think it is a pretty short time right now.

I don't really think freezing is a problem, but I will have to go some details about their valves etc with the operators to see what they say.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Neura Heat Pump Inverter Fault jimlong LIVE PLC Questions And Answers 8 May 11th, 2015 08:32 PM
program fault handler jude LIVE PLC Questions And Answers 21 February 19th, 2011 08:13 AM
RSLogix User Fault Routine jthornton LIVE PLC Questions And Answers 17 October 23rd, 2008 02:55 PM
TP177B + S7-300 on Profibus: No output happyhippo LIVE PLC Questions And Answers 23 May 15th, 2008 06:31 AM
Logic of Standby pump Shabbir LIVE PLC Questions And Answers 5 August 9th, 2002 11:00 PM


All times are GMT -5. The time now is 02:23 PM.


.