Off-scale 4-20mA reading when connected to PLC

Hi,
I'm a noob after some help if possible.
I have been using a Click PLC with a 0-20mA analog input module, quite happily, for some time now. I have been using 2 and 3 wire transmitters with no issue. The problem I am now experiencing is with a 4 wire transmitter that is powered from a supply separate to the PLC. I measure a steady 4mA, in the transmitter loop output, with a multi-meter but when I connect the loop output to the PLC (between channel input and 0V) the PLC reads over-scale i.e. status monitor shows maxed out at 20mA.
This has me confused - does anyone have any advice they can offer?
Is this anything to do with input impedance and could I need an additional resistor?
I would be greatly appreciative of any assistance.
Cheers,
  Reply With Quote
Old December 7th, 2017, 04:03 AM   #2
mbartoli
Member
United States

mbartoli is offline
 
Join Date: Sep 2007
Location: Cape Canaveral, FL
Posts: 142
Not familiar with the Click, but does it have two or three terminals on the input card? If only two, it may be limited to sourcing the loop power; check your documentation. If that is the case, you may have to use a loop isolator between the transmitter and the input. If there are three terminals, usually one is signal input, one is +DC supply and one is signal ground. If that is the case, use the Signal input and ground terminals. Since you are getting an over-scale indication, the field-powered loop is adding to the input card loop power and driving it off-scale high. Eliminating the two loop powers will correct this.
__________________
Mark

Those who say it cannot be done shouldn't interrupt the people doing it.
  Reply With Quote
Old December 7th, 2017, 05:38 AM   #3
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,138
Common problem with 0-20mA or 4-20mA devices that have non-isolated inputs. You either need to use a loop isolator as already suggested or you need to be able to tie the 0V of both supplies together.
  Reply With Quote
Old December 7th, 2017, 07:40 AM   #4
rpoet
Member
United States

rpoet is offline
 
Join Date: Jun 2008
Location: New York, NY
Posts: 444
Since you are already using AutomationDirect products:

https://www.automationdirect.com/adc...er_Input/FC-33

Phoenix Contact and many other manufacturers make ma-loop isolaters.

-rpoet
  Reply With Quote
Old December 7th, 2017, 09:42 AM   #5
shooter
Member
Netherlands

shooter is offline
 
shooter's Avatar
 
Join Date: Sep 2002
Location: duketown
Posts: 2,601
make sure the connection is correct, as it can be that the mA is controlled by the returning signal.
If this is gnded in two places, it will not be controlled.
Is a resistor present to measure the voltage?
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PanelView Plus communication loss if Flex I/O is connected with PLC toont LIVE PLC Questions And Answers 3 September 18th, 2015 11:25 AM
Connecting a weight and count scale to PLC docman24 LIVE PLC Questions And Answers 6 February 27th, 2015 08:16 AM
Reading selected language on PanelView by CompactLogix PLC amberman LIVE PLC Questions And Answers 2 December 4th, 2014 09:31 AM
Red Lion HMI not reading correctly a PLC tag. Elcan LIVE PLC Questions And Answers 4 May 18th, 2010 10:48 AM
Real World Problem Vietnam Bob LIVE PLC Questions And Answers 8 November 23rd, 2002 02:03 PM


All times are GMT -5. The time now is 02:25 PM.


.