Greetings to everyone,

my question is: How can I Read a thermpcouple typej ona an analog module (1762-if) on an allen bradley micrologix 1400 (rs logix 500) and convert the signal to temperature?

thanks in ahead
 
- A thermocouple doesn't measure an absolute temperature, it measure the difference between a hot junction and a cold junction and that module has no compensation for the temperature of the cold junction, and that introduces a big error.

- The voltage generated by a J thermocouple is at most 30-40 mV and with a input module with a range of -10V to + 10V the resolution you have will be horrible bad.

In other words, to connect thermocouples directly to a PLC, you need a thermocouple input module.

Another alternative is to use an intermediate converter/transmitter with J thermocouple input and 0-10V or current output
 

Similar Topics

I am having an issue getting a IY4 to read my thermocouple correctly. We have a R type and K type hooked up and sitting at a known room...
Replies
5
Views
462
Posted by u/mr_biodtox 44 minutes ago Delta ISPSoft - Establishing communication with thermocouple module Hi, How do I establish communication...
Replies
1
Views
313
Hi, We have an ongoing project with a lot of thermocouple involved that monitor the temperature of heaters. There are more than 20 PID...
Replies
32
Views
3,355
Hello. PLC beginner here, so apologies in advance for any incorrect terminology or poor communication. I have an SLC 500 Thermocouple/mV Analog...
Replies
1
Views
639
Hello Guys, Trying to scale a thermocouple directly into my IY4 card. Connected into the terminal +\-. I’ve scaled the range of my J type to...
Replies
4
Views
1,610
Back
Top Bottom