level switch vs pressure switch

Charbel

Member
Join Date
Jan 2012
Location
Beirut
Posts
307
Dear,

For protecting the pump against dry running, it is better to use low level switch in the tank or pressure switch on the suction side?

I tend to go for low level switch in the tank to protect the pump from dry run, please advise of any thought.

thank you!

charbel
 
I don't think one can say which is better. But I would go with the level switch.

Most tanks will have a low and high for control and a Low-low and High-High for protection. The extra switches provide extra protection if the low does not shut the pump off the low-low will.

Then again a pressure switch closed to the pump would protect against closed or pinched valves.

Your installation will dictate. Maybe you need both.
 
For protection against running dry the level switch, regardless of type, is probably the better bet. A low pressure (high suction) switch on the suction side of the pump would be used to protect against cavitation. If you have a flooded suction pump with normal piping that is probably not a problem.
 
Level switch is the simplest.

There is however another option to consider if level switch installation is challenging. www.loadcontrols.com has a sensor where you place a CT around a motor lead wire and it can detect pump dry run. It also works if someone closes the pump suction valve.
 
If you use a level switch, you probably also need a pressure switch because you might have a closed valve after the pump (liquid but no flow). If you use a flow switch you don´t need any other switch.
 
Dear,

I assume a flow switch will needs to be located after the pump, because a flap type flow switch before the pump will not make a difference but on the contrary it will stop the pump from running because the pump will need to run to make flow and to make the flow switch work.
I might use a thermal based switch on the discharge but am i not being too late to stop the pump?, the thermal based switch will have to detect no flow in order to stop the pump which is too late?

I think the best would be pressure switch on suction combined with low level switch on the upstream tank

Any thought about this?

Thank you!

charbel
 
I don't think I'd bother with the pressure switch at all

I think it would be more trouble than it would be worth

The flow switch can be a pain as well, and you will have to ignore it till you get the pump started

use floats
 
Well it all depends on your system actually.

If you have a foot valve installed (assuming tank is lower than pump) that would make sure your pump remains primed, just go for a low level switch.

If you choose to use a flow switch, I think you may have to bypass the flow safety system during pump starting and adjusting its suction/discharge valves. So low level is a good option I would say.

Hope this helps.
 
I also use a level limit switch model Liquiphant FTL20 (vibrating forks type) before the pump. If pipe empty, the pump won't run. Works all the time.
 

Similar Topics

Dear, I have a case where a centrifugal pump is sucking from a double compartment tank, usually for the dry run protection of the pump, we use...
Replies
15
Views
7,672
dear, i am assigning start/stop levels for the sump pump, i was wondering what is the minimum differential level that can be used when a float...
Replies
8
Views
2,561
Dear all, i have LS1200 murphy used for suction scrubber (connected NC contacts to 1756-IQ16 card) and the question is: when i triggered switch...
Replies
2
Views
1,717
Hi Guys, I wrote a Program on Tank Over fill Protection system. There are Five Tanks/Five Rosemount 2120 Level switch inputs and One Audio...
Replies
2
Views
1,555
Dear, I am trying to size level switch contact rating for a specific application. we will be using multilin 469 as below...
Replies
4
Views
1,869
Back
Top Bottom